    #1
  1. Join Date
    Jun 2014
    Posts
    1
    Reputation

    What is the insulation level of a cable marked MV-90/175mils?

    I incorrectly answered the following question. Can someone explain to me what the cable markings mean and provide a link? From reading online it looks like the marking means a medium voltage cable with a normal temperature rating of 90 degrees and an insulation thickness is 175mils. Is the insulation percentage a certain value since the cable is medium voltage? i.e. for MV anything above say 100mils is 100%, anything above 200mils is 133% and anything above 300 mils is 175%?

    • What is the insulation level of a cable marked MV-90/175mils?
    Correct Answer: 100%

    Thanks,

  2. #2
  3. Jay Knight is offline
    I have no flair
    Junior Member
    Join Date
    Apr 2014
    Posts
    19
    Reputation
    For medium voltage cables, insulation levels greater than 100% are intended to provide an additional safety factor for the un-faulted phase conductors in the event of a fault on one phase in a three phase system.

    Insulation thickness’ for medium voltage cables can be obtained from ICEA standards. Check out this link for more information:

    http://www.okonite.com/engineering/t...ws/Tech_27.pdf

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    Cable Insulation Thickness for Various Levels

    The specified insulation thickness for each insulation level is similar among various industry standards. The thickness varies with insulation level, generally becoming thicker as the insulation level increases.

    Click image for larger version. 

Name:	mv-cable-insulation-thickness-table.png 
Views:	67 
Size:	11.3 KB 
ID:	256

    Typical insulation thicknesses for many medium-voltage cables are shown in Table 1. Specific insulation thicknesses for voltage ratings up through 46 kV and various conductor sizes are given in National Electrical Manufacturers Association (NEMA), Insulated Cable Engineers Association (ICEA), Underwriters Laboratories (UL), Canadian Standards Association (CSA) and National Fire Protection Association (NFPA) publications.

    https://www.anixter.com/en_us/resour...on-levels.html

Subscribe

Share this thread

Related Topics

  1. Which is not required for 15kV inline cable splice?
    By madMAX in forum NETA Level 3 Exam
    Replies: 8
    Last Post: July 11, 2019, 11:18 AM
  2. What methods do you use for corona suppression when testing cable?
    By madMAX in forum Electrical Testing Talk
    Replies: 16
    Last Post: June 19, 2019, 01:01 PM
  3. Cable hi-pot withstanding time, why 15 minutes?
    By moon1958moon in forum Electrical Testing Talk
    Replies: 31
    Last Post: April 16, 2019, 06:37 PM
  4. Cable fault locating questions
    By adamwilson in forum NETA Level 3 Exam
    Replies: 4
    Last Post: October 25, 2016, 03:18 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net