What test voltage would you use on a maintenance test for an older switchboard with a nameplate voltage rating of 208/120? The reason I'm asking is because NETA table 100.1 shows a minimum test voltage of 500V for equipment with a 250V nominal rating. Would a 208V switchboard fall under that class, or is it still considered 600V class insulation? We usually test these boards at 1kV but I am wondering if we should do it at 500V.