Blocking capability and reduced voltage tripping are two tests listed for ground fault relays in NETA-ATS, can someone explain how these two tests are performed?
Blocking capability and reduced voltage tripping are two tests listed for ground fault relays in NETA-ATS, can someone explain how these two tests are performed?
Reduced voltage is accomplished with reduced control power voltage (we typically use 55%). This simulates what the ground fault control relay would have to function with if one of the legs feeding the control power transformer was grounded.
The blocking is, i believe, tested to ensure that the switch does not close back in on an active ground fault, or at least on an unacknowledged one.
Yep. Exactly.
NETA references zone-interlocking for the blocking capability test. Unless a restraint signal is used, any ground fault relay with zone interlocking will trip instantaneously regardless of the delay setting.
The restraint signal is normally applied with a small jumper between specified terminals on the ground fault relay -- consult the relay manufacturers literature for this procedure. Perform a time test with and without this signal applied to ensure proper operation.
ahh, thanks for the clarification.