    Here's why you should always short a CT secondary



    Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

    This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.

  2. #2
  3. Join Date
    Jan 2017
    Posts
    26
    Reputation
    Quote Originally Posted by SecondGen View Post


    Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

    This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.
    Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.

  4. #3
  5. Join Date
    Jan 2017
    Posts
    26
    Reputation
    Nice video btw

  6. #4
  7. Join Date
    May 2017
    Posts
    7
    Reputation
    Quote Originally Posted by codycody103 View Post
    Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.
    Wow! I have never tried that!

    And you can verify the secondary circuit integrity with the secondary injection function of my CT test set.

    See www.cttestset.com and read all about it.

  8. #5
  9. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by codycody103 View Post
    Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.
    Cody,

    Why do you mention "to remove shorting screws prior to energizing"? If you forget to remove them and energize the circuit, just remove them after energizing.

    Unless your point was to make sure you don't defeat your protection devices, then you would want to make sure shorting screws are removed before you walk away for good.

  10. #6
  11. lfmontoyas's Avatar
    lfmontoyas is offline Junior Member Pro Subscriber
    Join Date
    Aug 2017
    Posts
    7
    Reputation
    Quote Originally Posted by codycody103 View Post
    Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.
    Excellent video. Thank you.

  12. #7
  13. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by SecondGen View Post


    Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

    This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.
    Good post. Nice video, too. I was interested to see how the axe was going to come into play.

  14. #8
  15. Join Date
    Jan 2020
    Posts
    26
    Reputation
    This might be the most "hillbilly" safety video I've seen! haha

  16. #9
  17. Join Date
    Jan 2021
    Posts
    34
    Reputation
    I've always been told this but never had the visual, thanks for sharing!

Subscribe

Share this thread

Related Topics

  1. Replies: 8
    Last Post: April 12, 2018, 05:14 AM
  2. Cooling fans won’t stop running on transformer secondary side??
    By electrolyte in forum Electrical Testing Talk
    Replies: 1
    Last Post: October 22, 2016, 04:26 PM
  3. Replies: 0
    Last Post: March 1, 2016, 03:39 PM
  4. Important tip for measuring secondary current with AEMC PEL data logger