Contact resistance tester doesn't display any reading

 Jump to latest post
Page 1 of 2 12 LastLast
    #1
  1. lnides's Avatar
    lnides is offline Junior Member
    Join Date
    Jan 2016
    Posts
    6
    Reputation

    Contact resistance tester doesn't display any reading

    Hi, I just wanted to know how can I get the contact Resistance of Square D Circuit Breaker? When I test it the contact resistance tester didn't display any reading.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Could you provide more information, like the instrument model and troubleshooting steps? I'd hate to state the obvious but was the breaker closed and did you try different measurement scales? Try measuring a small piece of bus or cable to check the instrument.

  4. #3
  5. lnides's Avatar
    lnides is offline Junior Member
    Join Date
    Jan 2016
    Posts
    6
    Reputation
    square d type QOB 40 ampere 10kA 120/240V...Sometimes it gives a very low contact resistance like..0.00001milliohms,not stable..sometimes 19 milliohm..thank you..

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by lnides View Post
    square d type QOB 40 ampere 10kA 120/240V...Sometimes it gives a very low contact resistance like..0.00001milliohms,not stable..sometimes 19 milliohm..thank you..
    For a breaker of that size I would say 19 milliohms is probably the true reading. You might not be getting a stable reading because you are not making good contact with the test leads. All four test probes need to be making good contact with the (P) probes facing eachother.

  8. #5
  9. lnides's Avatar
    lnides is offline Junior Member
    Join Date
    Jan 2016
    Posts
    6
    Reputation
    Ah ok, Sir I Tested one this morning,,it has no continuity and contact resistance,but when I Injected it with 230V, It has an output of 230V..Is it ok?I mean is the Circuit Breaker ok for operation?

  10. #6
  11. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    I can't say whether the breaker is "ok for operation" because there is not enough information. It sounds like if you measure 19 milliohms on each pole the contacts are OK but you will have to inject 300% or 600% of rated current on each pole individually (40 * 3 = 120A / 40 * 6 = 240A) first and see if the breaker trips. Also do insulation resistance at 500V on each pole and make sure you get at least 25 megohms to ground.
    Last edited by SecondGen; February 2, 2016 at 02:14 PM.

  12. #7
  13. Join Date
    Jan 2015
    Posts
    48
    Reputation
    Charge your DLRO fully, check the connections on the test set, verify leads continuity (maybe even try with different leads) and try again.

  14. #8
  15. lnides's Avatar
    lnides is offline Junior Member
    Join Date
    Jan 2016
    Posts
    6
    Reputation
    Thanks Sir.

  16. #9
  17. Join Date
    Feb 2020
    Posts
    6
    Reputation

    Leads may be bad

    Check your leads I have had this happen, and it was because the leads had gone bad, swap yours with another tech and use thiers on your ductor , this may be your issue.

  18. #10
  19. Join Date
    Dec 2020
    Posts
    6
    Reputation
    Eaton doesn't recognize contact resistance on such small breakers because it is unreliable. Yes I know this is a SqD but the designs are so similar.
    Try doing a millivolt drop test when you inject rated current.
    If this is a used breaker, open and close the breaker 5-10 times while dead. This smashes any high spots on the contacts to give a better reading. Under load, the high spots melt until the current is more evenly spread.

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Do You Ever Grease Circuit Breaker Contacts?
    By alexlounsbury in forum Electrical Testing Talk
    Replies: 9
    Last Post: September 28, 2022, 10:41 AM
  2. Draw out circuit breaker positions, how many?
    By Mjeelemco in forum NETA Level 2 Exam
    Replies: 9
    Last Post: December 12, 2020, 07:54 AM
  3. When should circuit breaker contacts be lubricated?
    By zofofg in forum NETA Level 2 Exam
    Replies: 7
    Last Post: December 21, 2018, 07:27 PM
  4. Identify this circuit breaker symbol
    By MAKI2016 in forum NETA Level 2 Exam
    Replies: 10
    Last Post: September 27, 2017, 08:33 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net