Follow Us
Results 1 to 6 of 6

Minimum allowable work space around electrical equipment

 Jump to latest post
    #1
  1. DetroitLions is offline Junior Member Pro Subscriber
    Join Date
    Jan 2015
    Posts
    13
    Reputation

    Minimum allowable work space around electrical equipment

    Codes and Standards
    The minimum allowable work space around electrical equipment is _____ inches wide.

    Your Answer: 36
    Help: Article 110: Requirements for Electrical Installations

    According to this article the answer is 36 inches
    https://www.mikeholt.com/instructor2...239-sample.pdf

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Careful not to get width and depth confused.

    Width of Working Space.
    The width of the working space must be a minimum of 30 in., but in no case less than the width of the equipment.

    Click image for larger version. 

Name:	working-space-width-110.png 
Views:	580 
Size:	147.1 KB 
ID:	96

    Depth of Working Space.
    The working space, which is measured from the enclosure front, must not be less than the distances contained in Table 110.26(A)(1).

    Click image for larger version. 

Name:	working-space-depth-110.png 
Views:	750 
Size:	184.7 KB 
ID:	97

  4. #3
  5. Join Date
    Jan 2015
    Posts
    29
    Reputation
    Unless you have an engineer who has a electrical closet not big enough to swing a door open with an ATS and 2 subpanels in it

  6. #4
  7. Join Date
    Jul 2016
    Posts
    25
    Reputation
    What about for around battery banks? Do you measure from the front of the rack or the back of the rack?

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by copes2680 View Post
    What about for around battery banks? Do you measure from the front of the rack or the back of the rack?
    Working clearance is measured from the edge of a battery rack. NFPA-70 Article 480.9(C)

  10. #6
  11. Join Date
    Dec 2018
    Location
    Atlanta, GA
    Posts
    27
    Reputation
    Quote Originally Posted by SecondGen View Post
    Careful not to get width and depth confused.

    Width of Working Space.
    The width of the working space must be a minimum of 30 in., but in no case less than the width of the equipment.

    Click image for larger version. 

Name:	working-space-width-110.png 
Views:	580 
Size:	147.1 KB 
ID:	96

    Depth of Working Space.
    The working space, which is measured from the enclosure front, must not be less than the distances contained in Table 110.26(A)(1).

    Click image for larger version. 

Name:	working-space-depth-110.png 
Views:	750 
Size:	184.7 KB 
ID:	97
    I am a very visual person and this made it a lot easier to understand.

Subscribe

Share this thread

Related Topics

  1. Breathing patterns when performing hot work and switching
    By electrolyte in forum Safety and Arc Flash Talk
    Replies: 4
    Last Post: March 19, 2022, 12:36 PM
  2. Refusing to Work because Conditions are Dangerous (OSHA)
    By veracon0700 in forum Safety and Arc Flash Talk
    Replies: 0
    Last Post: January 6, 2016, 07:38 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net