    Contact resistance critera/passing range (low voltage air circuit breakers)

    Good Day!

    What is the criteria/passing range and standards for the Contact Resistance Test of Low Voltage Air-Circuit Breaker?

    Specs:
    ABB Manufactured with Iu=1600A, Ue=690V , 3 phase.....

    Among the 4 units I tested for its contact resistance, 3 of it has a higher values. Injected current is 100A AC.
    ACB #1 : 1435 micro ohms ; 1331 ; 847.7
    ACB #2 : 269.6 ; 790 ; 670.8
    ACB #3 : 22.8 ; 22.4 ; 22.3
    ACB #4 : 40.0 ; 39.6 ; 36.5

    Note that all ACB were at the same specs....


    Thank you.

    Godbless.

    Regards,
    Rizza

  2. #2
  3. Join Date
    Dec 2015
    Posts
    38
    Reputation
    Greetings Rizza! All three pases should be within 50% of the lowest value.

    Example: 22.3 being lowest value, contacts should not be higher than 33.45 (22.3 x 1.5).

  4. #3
  5. Join Date
    Jan 2016
    Location
    NJ
    Posts
    21
    Reputation
    at 100 amps...i would give those first two a good cleaning..should drop significantly

  6. #4
  7. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Junior Member
    Join Date
    Jan 2016
    Location
    Philippines
    Posts
    19
    Reputation

    @Sanjayo

    Thanks a lot. . .

    Is that from NETA standard?

    Regards,
    Rizza

  8. #5
  9. Join Date
    Dec 2015
    Posts
    38
    Reputation
    Yes, the +/- 50% rule comes from NETA. Are these new breakers?

    Quote Originally Posted by rizza_gay View Post
    Thanks a lot. . .

    Is that from NETA standard?

    Regards,
    Rizza

  10. #6
  11. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Junior Member
    Join Date
    Jan 2016
    Location
    Philippines
    Posts
    19
    Reputation

    Hello . . . .

    Quote Originally Posted by rizza_gay View Post
    Thanks a lot. . .

    Is that from NETA standard?

    Regards,
    Rizza

    Yes...those were new ACB. . .

  12. #7
  13. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Junior Member
    Join Date
    Jan 2016
    Location
    Philippines
    Posts
    19
    Reputation

    Good Day!

    Quote Originally Posted by Sanjayo View Post
    Yes, the +/- 50% rule comes from NETA. Are these new breakers?
    Yup...All breakers were new. One thing I've noticed is that the breakers were in Open Position before I conducted the test. Maybe, the presence of dusts in its contact matters.

  14. #8
  15. Join Date
    Dec 2015
    Posts
    38
    Reputation
    What kind of instrument are you using to measure?

  16. #9
  17. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Junior Member
    Join Date
    Jan 2016
    Location
    Philippines
    Posts
    19
    Reputation
    Quote Originally Posted by Sanjayo View Post
    What kind of instrument are you using to measure?
    Its the DV Power CAT66 : Circuit Breaker Analyzer

  18. #10
  19. Join Date
    Dec 2015
    Posts
    38
    Reputation
    Quote Originally Posted by rizza_gay View Post
    Its the DV Power CAT66 : Circuit Breaker Analyzer
    Did you say this was 100A ac? Using Dc current would give more stable reading.

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 6
    Last Post: July 11, 2020, 03:01 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net