At my company we were instructed to do the DC Transformer testing first (ie., Polarization Index, Winding Resistance) and the AC testing last (ie., TTR, Power Factor) because the AC changing polarity 120 times per second will wipe out any residual magnetic charge. Most Winding Resistance/Insulation Resistance test sets come with internal grounding to dissipate the magnetic charge anyway so for the most part it's a non-issue. Just remember to leave your test leads on until the test set has completed it's discharge.