Do you always pull circuit breaker arc chutes?

 Jump to latest post
    #1
  1. Join Date
    Dec 2014
    Posts
    19
    Reputation

    Do you always pull circuit breaker arc chutes?

    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.

  2. #2
  3. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    31
    Reputation
    Quote Originally Posted by wrh9278 View Post
    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.
    We do every time just to do a visual inspection. You would not believe how many times we've opened up a breaker and found loose hardware on a contact assembly or a missing contact pad on one of the arcing contacts etc. Im sure it varies upon job scope but i've never been on a job that we did not inspect the contacts.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Arc-chutes should always be removed. NETA maintenance specs say you should inspect circuit breaker moving and stationary contacts for condition, wear, and alignment. You should also inspect the individual arc-chutes for damage or signs of excessive arcing.

    If you really want to go by the book you should also verify that primary and secondary contact wipe and other dimensions vital to satisfactory operation of the breaker are correct. These might include sequence and pressure checks.

  6. #4
  7. Join Date
    Dec 2014
    Posts
    1
    Reputation

    Question to your question

    Quote Originally Posted by wrh9278 View Post
    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.
    How do you perform a slow close test with out removing the arc shoots? I would refer back to the manual of the breaker, and it will give you step by step on how they would perform their own maintenance

Subscribe

Share this thread

Related Topics

  1. Do You Ever Grease Circuit Breaker Contacts?
    By alexlounsbury in forum Electrical Testing Talk
    Replies: 9
    Last Post: September 28, 2022, 10:41 AM
  2. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 21, 2020, 01:32 PM
  3. Draw out circuit breaker positions, how many?
    By Mjeelemco in forum NETA Level 2 Exam
    Replies: 9
    Last Post: December 12, 2020, 07:54 AM
  4. When should circuit breaker contacts be lubricated?
    By zofofg in forum NETA Level 2 Exam
    Replies: 7
    Last Post: December 21, 2018, 07:27 PM
  5. Identify this circuit breaker symbol
    By MAKI2016 in forum NETA Level 2 Exam
    Replies: 10
    Last Post: September 27, 2017, 08:33 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net