    Having trouble with Omicron CT analyzer

    Good Afternoon...

    Has anyone of you here conducted a test for Bushing Type Current Transformers using an Omicron CT Analyzer???

    What is the reason if the CT Analyzer reflected after injecting:
    Test - OK but
    Assessment - Failed

    And some knee-points don't have values and some were at negative values. In addition to that, it also stated, "Inductance too low"

    Could you help me how to solve this situation?

    Thank you.

    Regards,
    Rizza

  2. #2
  3. Join Date
    Nov 2019
    Posts
    16
    Reputation
    "Inductance too low" - check if CT is shorted. Test set pre checks things and it has continuity, but doesn't see the inductance normally found with a CT in the circuit.




    Quote Originally Posted by rizza_gay View Post
    Good Afternoon...

    Has anyone of you here conducted a test for Bushing Type Current Transformers using an Omicron CT Analyzer???

    What is the reason if the CT Analyzer reflected after injecting:
    Test - OK but
    Assessment - Failed

    And some knee-points don't have values and some were at negative values. In addition to that, it also stated, "Inductance too low"

    Could you help me how to solve this situation?

    Thank you.

    Regards,
    Rizza

Subscribe

Share this thread

Related Topics

  1. Ripple Test of OLTC Auto-Transformer using Omicron CPC-100
    By rizza_gay in forum Electrical Testing Talk
    Replies: 0
    Last Post: March 30, 2016, 09:09 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net