    Why is the Network Protector phase relay tested at 60° angle?

    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?

  2. #2
  3. ironshovel77 is offline Junior Member Pro Subscriber
    Join Date
    Jan 2015
    Posts
    8
    Reputation

    nwp phase angle relay

    Quote Originally Posted by StoneyJ180 View Post
    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?
    I believe what testing at a 60 degree angle does is simulate a reverse power condition, which will trip the network protector.

  4. #3
  5. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    17
    Reputation

    What exactly is happening at 60°?

    Quote Originally Posted by StoneyJ180 View Post
    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?
    StoneyJ180,
    I hope you have gotten an answer before now! At 0° this would look like normal load current on the system,
    but the 60° shift would be an indication of a single-phase to ground fault. So this would be a fault condition qualifier for the relays response to trip or block operation.

Subscribe

Share this thread

Related Topics

  1. What will each wattmeter indicate?
    By Stephen30002 in forum NETA Level 3 Exam
    Replies: 7
    Last Post: January 6, 2021, 10:04 AM
  2. When would you most likely use a negative sequence relay?
    By Tseppish in forum NETA Level 3 Exam
    Replies: 4
    Last Post: October 9, 2018, 04:41 AM
  3. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: May 30, 2016, 03:25 PM
  4. Help understanding 3 phase electrical systems
    By randywright in forum Electrical Testing Talk
    Replies: 5
    Last Post: October 22, 2015, 11:46 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net