    EATON Magnum DS tripping free? Give this mechanism spring a check.

    Click image for larger version. 

Name:	magnum-ds-trip-free-how-to-fix.jpg 
Views:	14 
Size:	79.0 KB 
ID:	130

    There is a small retaining spring on the Magnum DS operating mechanism that can become worn and will break loose during a trip operation, causing a trip free condition on the next close operation. This one small spring is not held in by any retaining clips, and if it pops loose, you will never get the breaker closed again.

    Click image for larger version. 

Name:	magnum-ds-breaker-example-1.jpg 
Views:	158 
Size:	13.9 KB 
ID:	131

    I discovered this while primary-injecting a 4000A double-wide main breaker that had this issue. After running through the first couple of long time tests, the breaker started tripping free. I removed the face from the breaker, and after some looking, noticed a spring on the right side of the operating mechanism hanging off its pin.

    Click image for larger version. 

Name:	magnum-ds-trip-free-as-found-left.jpg 
Views:	19 
Size:	104.7 KB 
ID:	132

    As you can see in the photo, the spring keeps tension on the trip latch which must be pulled up after a charging operation. Connect the spring from the main pin on the trip latch and bring it up to the small pin just behind the close button (Push On). It's a poor design by EATON, as there are no retaining clips holding the spring in place.

    Click image for larger version. 

Name:	magnum-ds-trip-free-fix-location.jpg 
Views:	156 
Size:	31.9 KB 
ID:	133

    After putting the spring back where it belongs, the breaker closed but tripped free on the next test. I pulled the face off and found the spring hanging again! After comparing it to another from a spare breaker, it was obvious the spring was stretched out a bit and just didn’t have the tension necessary to stay in place.

    Click image for larger version. 

Name:	magnum-ds-trip-free-how-to-fix-2.jpg 
Views:	160 
Size:	73.5 KB 
ID:	134

    Keep in mind this was a 4000A main breaker feeding a critical switchboard. Luckily this was all found during regular maintenance. Just think, if this breaker would have tripped during normal operation, the customer would have never gotten it closed and would have been on generator until repairs could have been made.

    Ultimately I replaced the spring with one from a spare breaker and now the Main is working flawlessly. Isn't it amazing how one small part that probably cost less than $1 to manufacture could cause such a catastrophe? Hopefully this will help anyone in the field who runs into a Magnum DS that is tripping free.

  2. #2
  3. Kimbo Slice is offline Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    35
    Reputation
    Nice write up. Thanks for the info

Subscribe

Share this thread

Related Topics

  1. Do they give you a calculator for the NETA test?
    By wild turkey in forum NETA Level 2 Exam
    Replies: 10
    Last Post: April 20, 2020, 12:59 PM
  2. GE AK breaker intermittent nuisance tripping of bell alarm lockout
    By jdk0082 in forum Electrical Testing Talk
    Replies: 3
    Last Post: March 12, 2018, 02:26 PM
  3. EATON PX2000 Meter: How to Change IP Address in Power Xpert
    By SecondGen in forum Technical Documents
    Replies: 1
    Last Post: September 29, 2016, 05:07 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net