    hey all
    just kinda curious what methods the community uses to connect test leads (doble,ttr,megger,WR) to the high side of a transformer with load break elbows.

    Ive always gotta use a loadbreak elbow probe which has nothing to attach the hook to. I attach an alligator clip to the end of the probe and connect to that. Im sure there's something better out there.

  2. #2
  3. GavinK5's Avatar
    GavinK5 is offline Junior Member
    Join Date
    Aug 2015
    Posts
    18
    Reputation
    If you can get your hands on some old elbows the best thing to do is cut the probes out of those. Bolt a lug on the end of them and you have yourself a set of test pins that will plug right into the transformer, then you can clip your leads to the lugs. A set of 4 should cover most applications.

    Click image for larger version. 

Name:	1444897584_Load Break Elbows.jpg 
Views:	123 
Size:	47.1 KB 
ID:	171

  4. #3
  5. JP1946 is offline Junior Member
    Join Date
    Jan 2016
    Posts
    2
    Reputation
    We put all-thread couplings on the threaded end of an old test probe and put an eye bolt in the other side of the coupling. Makes it easier to pull out of the bushing.

Subscribe

Share this thread

Related Topics

  1. Safely discharge HV feeder using load break disconnect switch (procedure)
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 3
    Last Post: August 17, 2020, 01:08 PM
  2. Danger after lockout of GE Power Break equipped with electric charge
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 0
    Last Post: April 11, 2016, 02:38 PM
  3. Calibrating Allen-Bradley 810 oil-filled motor overload relay
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 1
    Last Post: June 30, 2015, 08:47 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net