    #21
  1. RabbleRabble is offline Member Pro Subscriber
    Join Date
    Apr 2020
    Posts
    28
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    I would disagree on one point. 7200V would be your VL-L and 4157.044V would be your VL-G. Anytime you read voltage on a WYE system, phase to phase (line to line) will be a larger number than your phase to ground (line to ground).

    (VL-L/sqrt(3)) = VL-G
    Great answer thank you. I think line to neutral voltages can be confusing.

  2. #22
  3. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by franko26 View Post
    Transformers
    A wye-delta transformer has a primary voltage of 7200 V and a secondary voltage of 360 V. What is the turns ratio?
    Your Answer: 1:20

    The test considered this answer wrong. The primary to secondary voltage ratio is 1 to 20. I'm sure the correct answer is 20:1, but grammatically speaking, the 1:20 answer is more correct. The following is from the noted study material:

    Since there is a ratio of 1 to 4 between the turns in the primary and secondary circuits, there must be a ratio of 1 to 4 between the primary and secondary voltage and a ratio of 4 to 1 between the primary and secondary current. Please advise.
    7200/1.732=4157
    4157/360=11.5

  4. #23
  5. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by stevenl569 View Post
    You are 100% correct on this. 7,200V (Line) WYE = 4,160V (Phase). On the Delta side Vline=Vphase. You should always use the phase voltages to get a ratio, especially when dealing with a WYE-Delta configuration. Using phase voltages your math should be 4,160V/360V = 11.55:1 Ratio not 1:11.55. Turns ration is stated with the Primary Turns First. So in this case the Primary voltage is higher so the ratio will begin with the higher number of turns.
    thats right

  6. #24
  7. ranniery100 is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    1
    Reputation

    Question is wrong?

    I believe this question is wrong. On D-D system there's only Line voltage. So the answer it's a direct division between the two available voltages 7200/360 = 20:1.

    On Y-D, you must divide the Line voltage on the primary to get the related phase voltage. In the secondary there's only one available voltage, which is the Phase one. So, the \TTR would be 7200/sqrt(3) / 480 = 11.55:1

Page 3 of 3 FirstFirst 123
Subscribe

Share this thread

Related Topics

  1. Saturation test of a 1500/5 multi-ratio CT
    By Tseppish in forum Electrical Testing Talk
    Replies: 11
    Last Post: August 4, 2021, 10:21 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net