Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
60,000 A
54,500 A
42,000 A
37,500 A
25,000 A
first should be 480Y/277 not 277y/480.
basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
z= (100/5)= 20
short circuit = 3007.08*20= 60189
so i would just go with the closest answer correct? and also they should fix the error on 277Y.