Thanks for the input. Here are some answers
Please correct me if I'm wrong:
1.A (Optic time domain reflectometry)
5.C
7. You did not specify the xfmr connection but assuming it is Delta/Wye my calculation is 3007.12 A primary
8. 5th Harmonic
10. Methane (Duval's Triangle)
11. 0.41 miliohms
12. 60A / sqrt(3) = 34.64A
On a Wye connection your phase current is equal to your line current but in a delta it is divided by 1.732
13. 1825.8 @ 0.91 PF
14. Requires no connection to ground (earth)
15.B (not required, NEC 700.6(D))
16.C (most likely since CAT6 length limit is 100 m)
17.B
18.A
19.C
20. Dielectric withstand @ 75% of Factory acceptance testing value (IEEE C37.20.6)
22.D (C200 since i came up with a burden of aprox 1.25 ohms which exceed the error limit of a C100)
24.B (0.89 vs 0.92)
25 The line reactor compensates for line capacitance, mitigates voltage transients and limits the fault currents. I don't know what the answers were there.
26. They are used in PLC (Power Line Carrier) to trap the high frequency communication signals typical of 400 Hz
29.D maybe? (Lead-acid is 5 years and VRLA 12-18 months so we need more info here)
31. 2.3 micro-farad