    Zone ground fault protection. Blocking and tripping?

    A substation has zone ground fault protection. Which statement is true?

    a. The main will trip before the feeder breakers
    b. The feeder breakers send a block to the main and tie so they don’t trip
    c. The feeder breakers send a block the main and tie so they don’t trip until their designated tripping time.
    d. The main will trip and block tripping to the other side of the bus

    It is my understanding that when zone interlocking is not defeated the breaker will trip at its minimum time no matter what. Defateating zone interlock will allow the breaker to trip at its programmed time delay. My answer would be "C". Can someone help verify this answer?

  2. #2
  3. Join Date
    Jun 2017
    Posts
    4
    Reputation
    Quote Originally Posted by marvinray View Post
    A substation has zone ground fault protection. Which statement is true?

    a. The main will trip before the feeder breakers
    b. The feeder breakers send a block to the main and tie so they don’t trip
    c. The feeder breakers send a block the main and tie so they don’t trip until their designated tripping time.
    d. The main will trip and block tripping to the other side of the bus

    It is my understanding that when zone interlocking is not defeated the breaker will trip at its minimum time no matter what. Defateating zone interlock will allow the breaker to trip at its programmed time delay. My answer would be "C". Can someone help verify this answer?
    From what I've researched you are correct. For ground fault zone protection, the closest protective device to the fault will trip instantaneously and send a signal upstream to start a time delay on the upstream device. Though each device can trip instantaneously, depending on the location of the fault. Hope this helps.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    I agree that the answer is C. Option B is close but wrong because it implies that the main and tie will never trip.

    When a device equipped with Zone-Selective Interlocking (ZSI) senses a short circuit or ground fault, it sends a restraint signal (via the restraint wires) to the ZSI device just upstream from it. This activates the preset time delay on the upstream device.

    When a device equipped with ZSI senses a short circuit or ground fault and does not receive a restraint signal, its preset time delay will not be activated and it will trip with no intentional delay.

    The system is designed to limit fault stress on the electrical distribution equipment by reducing the time it takes to clear the fault while maintaining system coordination between overcurrent and ground-fault protective devices.

    Click image for larger version. 

Name:	zsi-operating-principle.png 
Views:	10 
Size:	43.1 KB 
ID:	209

    Here are a couple documents that explain Zone-Selective Interlocking schemes in great detail:
    http://www2.schneider-electric.com/r...0600DB0001.pdf
    http://es.eaton.com/protectiverelays...P02602002E.PDF

  6. #4
  7. Join Date
    Apr 2017
    Posts
    15
    Reputation

    Ground Fault Zone Interlocking

    Quote Originally Posted by marvinray View Post
    A substation has zone ground fault protection. Which statement is true?

    a. The main will trip before the feeder breakers
    b. The feeder breakers send a block to the main and tie so they don’t trip
    c. The feeder breakers send a block the main and tie so they don’t trip until their designated tripping time.
    d. The main will trip and block tripping to the other side of the bus

    It is my understanding that when zone interlocking is not defeated the breaker will trip at its minimum time no matter what. Defateating zone interlock will allow the breaker to trip at its programmed time delay. My answer would be "C". Can someone help verify this answer?
    Yes, you are correct!

Subscribe

Share this thread

Related Topics

  1. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 02:46 PM
  2. Replies: 3
    Last Post: January 13, 2016, 01:39 AM
  3. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM
  4. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 5, 2015, 09:56 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net