    Megger Insulation Tester "br.d" Error Code

    Does anyone know what "br.d" means on the megger MIT 515? Got this error code today measuring a open vacuum bottle line to load. After pressing the TEST button the instrument showed the error right away. I have never seen this code before.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    Megger error codes

    Here are some common on-screen warning codes for Megger:

    Click image for larger version. 

Name:	megger-brd-error.jpg 
Views:	4361 
Size:	16.5 KB 
ID:	178

    br.d = Breakdown detection

    If insulation breakdown is detected, the unit aborts the test and flashes “brd” and the final test result alternately in the main digital display. This display is disabled when in burn mode as the unit will continue the test without aborting. The instrument detects breakdown in terms of a rapid drop in test voltage commensurate with that caused by an arc across or though the insulation under test.

    In breakdown mode the test will automatically terminate on detection of a breakdown to prevent damage to the insulation. Burn mode disables the normal breakdown detection and test voltage continues after breakdown of the insulation. This enables the location of the failure to be seen and detected acoustically but it is a destructive test


    Click image for larger version. 

Name:	megger-excessive-noise.jpg 
Views:	4335 
Size:	6.0 KB 
ID:	179

    nSE = Extremely High Noise

    Should an extremely high level of noise be present, particularly at the start of a test, the instrument will indicate nSE (Noise). The instrument will require switching off and on again to reset. In certain rare circumstances breakdown of the circuit under test may interfere with the sensitive current measuring circuit. In this event the unit stops and also displays nSE. The instrument will again require switching off and on again to reset.


    Click image for larger version. 

Name:	megger-nosie-detected.jpg 
Views:	4324 
Size:	16.4 KB 
ID:	180

    (Waveform) = Noise Detected

    A level of noise exceeding the instruments specified capability will be indicated by an alternating sine wave on the display. The test continues while displaying the noise. If the noise drops back down the normal display is resumed. The black and grey waveforms are displayed alternately while the noise is present. When the noise is removed the wave form is replaced by the correct reading.


    Source comes from a Megger MIT 1020 manual but I would imagine they would be the same for MIT 515. Here is the link http://www.pmc-rentals.com/wp-conten...User-Guide.pdf

  4. #3
  5. Join Date
    Dec 2021
    Posts
    1
    Reputation

    About br.d error

    Quote Originally Posted by iwanttotest View Post
    Does anyone know what "br.d" means on the megger MIT 515? Got this error code today measuring a open vacuum bottle line to load. After pressing the TEST button the instrument showed the error right away. I have never seen this code before.
    Pl. Check high voltage realy in high voltage section. Un plug two red clip. Sparking is in realy gives this massage.
    Thanks.

  6. #4
  7. Join Date
    May 2017
    Posts
    16
    Reputation
    Quote Originally Posted by iwanttotest View Post
    Does anyone know what "br.d" means on the megger MIT 515? Got this error code today measuring a open vacuum bottle line to load. After pressing the TEST button the instrument showed the error right away. I have never seen this code before.
    Not trying to be a wise a$$.

    Insure the breaker is really open.
    Check across the bottle with something else.
    May be a bad bottle.

    The megger seems to think so.

  8. #5
  9. tmx1911 is offline Junior Member Pro Subscriber
    Join Date
    Sep 2021
    Location
    Peoria, IL
    Posts
    5
    Reputation
    Quote Originally Posted by iwanttotest View Post
    Does anyone know what "br.d" means on the megger MIT 515? Got this error code today measuring a open vacuum bottle line to load. After pressing the TEST button the instrument showed the error right away. I have never seen this code before.
    I have had an issue with the Megger Instruments going into "BrD" breakdown mode with transformers. I assume this is because of capacitance.

    To work around this I have switched the unit from it's default mode to "BURN" mode which disables the breakdown function.

Subscribe

Share this thread

Related Topics

  1. Megger Insulation Tester 'UNC' Error
    By websterd in forum Electrical Testing Talk
    Replies: 2
    Last Post: January 13, 2020, 03:54 PM
  2. Help with calculating percent error
    By trhea@saberpower.com in forum NETA Level 2 Exam
    Replies: 7
    Last Post: October 24, 2017, 05:21 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net