Needed Utility Information:
1. Three-phase short circuit MVA and X/R ratio at the transformer primary for each incoming service if they are different.
3-Phase MVAsc _______________
X/R Ratio __________
2. Single line-to-ground short circuit MVA and X/R ratio at the transformer primary for each incoming service if they are different.
SLG MVAsc _______________
X/R Ratio __________
3. Nominal, lowest, and highest kV at the point of service during the last 2 years.
4. Phase Overcurrent Relay for each service:
Manufacturer and Type:
CT and Settings:
(If protective device is fuse, please provide fuse Type and Size.)
5. Ground Overcurrent Relay for each service:
Manufacturer and Type:
CT and Settings:
6. If there is transformers belonging to utility, please provide following information for each transformer:
Transformer rating:
Impedance:
Type of cooling (OA/FA?)
Temperature rating (55 C/65 C?)
Connection type.