  1. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation

    High Current Injection LTD Test Value

    I disagree that my answer was wrong. The question:

    7. To test the long time delay function of a breaker which is set for 1000 amps ___________ test current is needed.
    From memory answers were:
    a. 1000A
    b. 1500A
    c. 3000A
    d. Need more information

    I chose D, because both B and C could be correct. I also wondered if it was a trick question with the wording. LTD is set in time, they don't specify that 1000 amps is the LT pickup. My answer was marked wrong. If LTD was always to be tested at 3x, then we wouldn't need TCC's, just a standard range. I've tested a 4000a breaker at 8000 to keep a test set from overheating. It would take a lot of time, but I could test the long time function of a 1000a pickup at 1500 amps.

    I dislike that in some questions, tricks are tricks, yet in others, the generic standard seems to be the right answer.

    Anyone else stumble on this?

  2. #2
  3. Join Date
    Jan 2016
    Posts
    1
    Reputation

    It would be C

    You could test the pickup value at 1000, but the question ask for time delay which would be 3x the rated current which would be the answer C, 3000.

  4. #3
  5. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation
    Quote Originally Posted by Mcfly89 View Post
    You could test the pickup value at 1000, but the question ask for time delay which would be 3x the rated current which would be the answer C, 3000.
    You could test the time delay at 3x. You could also test it at 1.5x, 6x, 10x... We have TCC's to chart every level of current flow, 3x is just a standard that's been used for convenience. NETA doesn't require 3x, nor does any other governing body that I've seen.

    Just because a practice is common doesn't mean it's a rule.

  6. #4
  7. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    18
    Reputation
    Quote Originally Posted by alexlounsbury View Post
    You could test the time delay at 3x. You could also test it at 1.5x, 6x, 10x... We have TCC's to chart every level of current flow, 3x is just a standard that's been used for convenience. NETA doesn't require 3x, nor does any other governing body that I've seen.

    Just because a practice is common doesn't mean it's a rule.
    This was talked about at the Neta conference and it was agreed that there is no standard for this type of question.

  8. #5
  9. Join Date
    Apr 2017
    Posts
    15
    Reputation

    Circuit Breaker Primary Injection

    Quote Originally Posted by alexlounsbury View Post
    I disagree that my answer was wrong. The question:

    7. To test the long time delay function of a breaker which is set for 1000 amps ___________ test current is needed.
    From memory answers were:
    a. 1000A
    b. 1500A
    c. 3000A
    d. Need more information

    I chose D, because both B and C could be correct. I also wondered if it was a trick question with the wording. LTD is set in time, they don't specify that 1000 amps is the LT pickup. My answer was marked wrong. If LTD was always to be tested at 3x, then we wouldn't need TCC's, just a standard range. I've tested a 4000a breaker at 8000 to keep a test set from overheating. It would take a lot of time, but I could test the long time function of a 1000a pickup at 1500 amps.

    I dislike that in some questions, tricks are tricks, yet in others, the generic standard seems to be the right answer.

    Anyone else stumble on this?
    Since you are taking the NETA exam you need to follow as per NETA table 100.7 Inverse Time Trip Test
    at 300% of Rated Continuous Current of Circuit Breakers

  10. #6
  11. Join Date
    Apr 2017
    Posts
    15
    Reputation

    CB Testing

    Quote Originally Posted by alexlounsbury View Post
    I disagree that my answer was wrong. The question:

    7. To test the long time delay function of a breaker which is set for 1000 amps ___________ test current is needed.
    From memory answers were:
    a. 1000A
    b. 1500A
    c. 3000A
    d. Need more information

    I chose D, because both B and C could be correct. I also wondered if it was a trick question with the wording. LTD is set in time, they don't specify that 1000 amps is the LT pickup. My answer was marked wrong. If LTD was always to be tested at 3x, then we wouldn't need TCC's, just a standard range. I've tested a 4000a breaker at 8000 to keep a test set from overheating. It would take a lot of time, but I could test the long time function of a 1000a pickup at 1500 amps.

    I dislike that in some questions, tricks are tricks, yet in others, the generic standard seems to be the right answer.

    Anyone else stumble on this?
    As per NETA it should be 300%, testing at 150% or 200% will overheat and damage a circuit breaker, especially on a molded case circuit breaker.

Subscribe

Share this thread

Related Topics

  1. Primary Current Injection instantenous Pickup
    By changeabilities in forum Electrical Testing Talk
    Replies: 15
    Last Post: February 26, 2021, 11:50 AM
  2. Primary Current Injection Test
    By changeabilities in forum Electrical Testing Talk
    Replies: 4
    Last Post: August 12, 2018, 08:17 AM
  3. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM
  4. How to Test Breaker through Current Injection Tester ?
    By mask1290 in forum Electrical Testing Talk
    Replies: 8
    Last Post: September 19, 2017, 06:57 PM
  5. Looking for high current testing standard for breakers