Contact resistance test producing CT secondary current

 Jump to latest post
    #1
  1. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation

    Contact resistance test producing CT secondary current

    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    How did they test the breaker? I am assuming it was connected in normal position with line bus de-energized and contact-resistance was measured from line bus to load bus.

    As far as finding a peer reviewed article is concerned, I don't know of any but I can ask some relay guys if they have ever seen anything like what your describing. You might be able to contact the manufacturer of the test set for an answer. Your experiment sounds interesting and I would love to see the result.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    So after talking with some of the guys at my shop, everyone seems to agree that your theory is plausible but more information is needed about the scheme to know what really happened. It's also possible that there is a wiring problem somewhere which caused the breaker to trip.

    Can you provide a sketch of the differential protection scheme along with relay settings and the location of the DLRO test leads? This will help to better understand the various zones of protection.

  6. #4
  7. Join Date
    Apr 2017
    Posts
    15
    Reputation

    Differential Trip

    Quote Originally Posted by alexlounsbury View Post
    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Review your SLD, check the Zone of protection what equipment are associated with the differential scheme.

  8. #5
  9. Achandler is offline Junior Member
    Join Date
    Sep 2017
    Posts
    16
    Reputation
    Quote Originally Posted by Skyehaven40 View Post
    Review your SLD, check the Zone of protection what equipment are associated with the differential scheme.
    This is an interesting topic, has anyone discovered the cause of the differential trip?

  10. #6
  11. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    17
    Reputation

    DLOR Demon!

    Quote Originally Posted by Achandler View Post
    This is an interesting topic, has anyone discovered the cause of the differential trip?
    This problem has reared its ugly head many times over the years. While performing this resistance check, the current was increased from 0 to 200 amps. After getting the readings, the test set was turned off. Not ramped down, just shut down. The bus diff saw this 200 amps to zero spike as an input from the out of service breaker and out went the bus.

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by alexlounsbury View Post
    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Hey alexlounsbury, I know its been a while but here is a paper from Megger that discusses your exact problem:

    Effects of Low Resistance Measurement Instruments on Protection and Control Devices, Effect of DLRO on the differential protection scheme

    The DC current used for measuring the low resistance can affect the protection and control circuitry in adverse ways. Typical problems encountered are Current Transformer (CT) magnetization, accidental tripping of differential relays and inconsistent and unreliable low resistance measurements. The paper will address the root cause of these encountered problems. It will recommend precautions to take prior to performing the test and discuss in detail the recommended practices to avoid any misoperation of connected protection and control devices.

    https://content.megger.com/getattach...ol-Devices.pdf
    Last edited by SecondGen; July 12, 2018 at 07:24 PM.

  14. #8
  15. Join Date
    Dec 2014
    Location
    Houston, TX
    Posts
    11
    Reputation
    Quote Originally Posted by alexlounsbury View Post
    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Was this using a 10A ductor or a larger 100-200A unit?

  16. #9
  17. Join Date
    Aug 2018
    Posts
    6
    Reputation

    M

    Quote Originally Posted by alexlounsbury View Post
    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Our crew, when ductoring a breaker associated with any bus config, have isolated the breaker and shorted the CTS
    's indicative of the protection schemes. Just because I've heard of such things happening.

  18. #10
  19. Join Date
    Nov 2019
    Posts
    16
    Reputation
    Quote Originally Posted by SecondGen View Post
    Hey alexlounsbury, I know its been a while but here is a paper from Megger that discusses your exact problem:

    Effects of Low Resistance Measurement Instruments on Protection and Control Devices, Effect of DLRO on the differential protection scheme

    The DC current used for measuring the low resistance can affect the protection and control circuitry in adverse ways. Typical problems encountered are Current Transformer (CT) magnetization, accidental tripping of differential relays and inconsistent and unreliable low resistance measurements. The paper will address the root cause of these encountered problems. It will recommend precautions to take prior to performing the test and discuss in detail the recommended practices to avoid any misoperation of connected protection and control devices.

    https://content.megger.com/getattach...ol-Devices.pdf


    I know a long time ago this was also discussed at a Doble convention. If you are a Doble client, you can check the website for the paper.

    Additional word of caution. When you short out Hi Z bus diff CT's, you are shorting out the protection for the whole bus!! Best to lift the leads at the summation box (if it exists).
    Last edited by Realtime; April 7, 2021 at 10:40 AM.

Subscribe

Share this thread

Related Topics

  1. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 21, 2020, 01:32 PM
  2. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 6
    Last Post: July 11, 2020, 03:01 PM
  3. Replies: 8
    Last Post: April 12, 2018, 05:14 AM
  4. Replies: 11
    Last Post: March 31, 2016, 02:26 PM
  5. Important tip for measuring secondary current with AEMC PEL data logger
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: October 8, 2015, 12:19 PM