I've done this one multiple times. Candy thermometer and a metal coffee can and a torch.
Use what you've got.
I've done this one multiple times. Candy thermometer and a metal coffee can and a torch.
Use what you've got.
Step 1: Calculate the needed Voltage Drop by subtracting the 2 voltages
125V - 24V = 101V
Step 2: Calculate the needed Resistance using ohms law: R = V / I
101V / 0.500 = 202 Ohms
Step 3: Calculate Resistor Wattage from the Current and Resistance using P = I2R
0.500 x 0.500 x 202 = 50.5W
Best answer here would be no separate source of control power. Network Protectors obtain control power from the network transformer secondary.
Westinghouse NWP's, for example, use a control power transformer while GE taps right off the line and steps down voltage with resistors. In either case, the network transformer supplies voltage. If the transformer goes down, there is no other source for control power.
B and D are just plain wrong, network protectors don't utilize contactors for operation.
A) Increases between 0 and 90 degrees - Phase angle would be getting larger, with difference in potential (voltage) increasing.
B) Increases between 180 and 270 degrees - Phase angle would be getting smaller (moving towards zero) because its now past 180 degrees, voltage would be decreasing.
C) Decreases between 180 and 90 degrees - Phase angle would be moving back towards zero, voltage would be decreasing.
D) Decreases between 90 and 0 degrees - Phase angle would be doing same as above, moving closer to being in phase (0 volts) meaning voltage is decreasing.
Best answer is A.
According to the NFPA 70, what is the max allowable time delay results for a ground fault relay to operate?
A) 1 second at 1200 amps
B) 3 sec at 3000 amps
C) 5 sec at 1200 amps
D) At the actual available fault current
i found that the book said 1 sec at 3000+ amps
This is what I found also, so there is technically a right answer. Has any one called out NETA on this? I am finding a lot of questions that don't have a right answer or two right answers. Anyone else feel they are making these tests arbitrary, and like they are written be a six year old? Frustrating.
I so agree with you it seems the tests have been made to fail and cost the companies more money and time having you take the test two and three times
i would say the answer is A i know that this the max setting by NEC and the max clearing time is 1 sec at 3000 amps its the only answer close very badly worded question
I see A as being a possible answer. The ATS that I have worked with have an interlock that will not allow the ATS to close in to the generator if the breaker feeding it from the utility side has not opened. This keeps your generator from feeding back to the utility or down the street to the linean trying to repair the lines.
An automatic transfer switch is an open transition (break before make) when using it on a utility and generator. Therefore, your ATS is already preventing a backfeed to your utility. There is no need to open the feeder breaker. It is possible it were spec’d That way for your job, but extra control wires would need to be run to monitor breaker status and remote close and trip from the ATS. This is not a common practice. “A” is definitely not the correct answer on a test