This one was also on mine and one of the choices was 1 sec at 3000 amps which is exactly what you found. I would like to know what book it was found in??
The answer is Density. I remember this bening a topic of discussion from one of the pop quizzes in the NETA World publications in the last couple years. Its also somewhere in the study guide that NETA has. The one with a combined set of pop quizzes from all past issues.
I humbly disagree with NoWorldOrder in that the question states that the generator is running and is at voltage. If the system is monitoring a different phase than a 'single phase event', there would be no start command to the genset. I believe the answer is that frequency is not in the transfer band to give the ATS a permissive. IMHO anyways, for what that might be worth.
See NEC 230.95 (A) Max pick up setting is 1200A. Maximum time delay is 1 sec for fault current of 3000A or more. What the answers seem to imply is that 1 second it the maximum delay from pick up setting to 3000A. Most GFR's I can think of on bolted pressure switch setups have a definitely time delay after pickup with max of 1 sec, so the time delay would be 1 sec at 1200A pickup. Electronic breakers with GF can have I^2T slope functions, and the knee point at pickup can be above 1 sec, but is always below 1 sec by 3000A. But this would allow for a timing at a 1200A pickup of 2 secs in many cases. Code only specifies that the time delay has to be 1 second or less at 3000A.