Level III Questions, seen recently (from memory bear with me), help?

 Jump to latest post
Page 4 of 4 FirstFirst ... 234
    #31
  1. Join Date
    Nov 2016
    Posts
    6
    Reputation
    Quote Originally Posted by jwdrowe View Post
    According to the NFPA 70, what is the max allowable time delay results for a ground fault relay to operate?
    A) 1 second at 1200 amps
    B) 3 sec at 3000 amps
    C) 5 sec at 1200 amps
    D) At the actual available fault current
    i found that the book said 1 sec at 3000+ amps
    This one was also on mine and one of the choices was 1 sec at 3000 amps which is exactly what you found. I would like to know what book it was found in??

  2. #32
  3. Join Date
    Nov 2016
    Posts
    6
    Reputation

    SF6 Gage measures what?

    Quote Originally Posted by dvansick2345 View Post
    I would of said density or level but I'm not sure
    The answer is Density. I remember this bening a topic of discussion from one of the pop quizzes in the NETA World publications in the last couple years. Its also somewhere in the study guide that NETA has. The one with a combined set of pop quizzes from all past issues.

  4. #33
  5. Join Date
    Feb 2018
    Posts
    4
    Reputation
    Quote Originally Posted by NoWorldOrder View Post
    The correct answer is D. All I can think of is that the question is asking about an ATS that is only monitoring one phase. Also to consider, in MTM transfer schemes (which I've written the logic for many times) the end-users do not want a transfer on a single phase going to ground. They want the HRG to handle it and then to let the motors run on two phases while they track it down.

    Anyway, the correct answer is D. Had the same question.
    I humbly disagree with NoWorldOrder in that the question states that the generator is running and is at voltage. If the system is monitoring a different phase than a 'single phase event', there would be no start command to the genset. I believe the answer is that frequency is not in the transfer band to give the ATS a permissive. IMHO anyways, for what that might be worth.

  6. #34
  7. Join Date
    Feb 2019
    Location
    Reno, NV
    Posts
    2
    Reputation
    Quote Originally Posted by SecondGen View Post
    Step 1: Calculate the needed Voltage Drop by subtracting the 2 voltages

    125V - 24V = 101V


    Step 2: Calculate the needed Resistance using ohms law: R = V / I

    101V / 0.500 = 202 Ohms


    Step 3: Calculate Resistor Wattage from the Current and Resistance using P = I2R

    0.500 x 0.500 x 202 = 50.5W
    Late to the game response, I know, but you don't even need to calculate the resistance. Do the KVL to figure out voltage drop of 101 volts, then multiply by 500mA since total current flows through both components, and power is as easy as PIE (P=I x E).

  8. #35
  9. Join Date
    Dec 2018
    Posts
    1
    Reputation
    Quote Originally Posted by ElectricalTestTech View Post
    Well here is my attempt at helping you. Someone please feel free to correct me if I'm wrong.

    1. What is an application for a circuit switcher with a pre-insertion inductor?
    A) Transient control w/ high fault currents
    B) Transient control for capacitor bank switching
    C) Current damping at 12.4kV
    D) Current damping above 34.5kV

    A pre-insertion inductor arrangement is provided for a circuit switcher to reduce audible and electrical noise and to limit transient inrush current and/or voltages upon closing of the circuit by the circuit switcher. Pre-insertion inductors have been introduced as a cost-effective alternative to pre-insertion resistors for controlling capacitor bank energization overvoltages.

    I have to go with B

    2. How is lagging power factor improved using a synchronous motor?
    A) Raise excitation of field windings
    B) Lower excitation of field windings
    C) Raise excitation of amortisseur winding
    D) Lower excitation of amortisseur winding
    A Synchronous Motor can be made to operate at unity and leading power factor by just increasing its excitation voltage by increasing the field current. I believe the answer is A. But someone please chime in on this one
    In the old days the utility used synchronous motors to control reactive power. They would not drive a load. By control of the excitation current they could off-set and bring the power factor close to unity.

  10. #36
  11. jfoster is offline Junior Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    11
    Reputation
    Quote Originally Posted by cjones09 View Post
    Looking for help on this question. These are my thoughts, what do you think?

    A. This could be possible, the question doesn't state if the utility available light is still on or not
    B. Not sure what type of ATS we are dealing with
    C. Question doesn't specify the application but I would think any sync issues would be resolved at the gen switchboard
    D. This would be a cause for transfer, so this answer is probably incorrect

    Thanks in advance.
    My though is that a battery should not be involved with an ATS, loss of phase should cause a transfer. I would think it would be a sync check issue. If it could not sync it would not transfer.

  12. #37
  13. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation
    Quote Originally Posted by ray12taylor View Post
    This one was also on mine and one of the choices was 1 sec at 3000 amps which is exactly what you found. I would like to know what book it was found in??
    Wouldnt it be 1 second at 1200amps? The max allowable ground fault setting is 1200amps.

  14. #38
  15. Join Date
    Apr 2018
    Location
    Michigan
    Posts
    40
    Reputation
    Quote Originally Posted by Warrengarber View Post
    Wouldnt it be 1 second at 1200amps? The max allowable ground fault setting is 1200amps.
    See NEC 230.95 (A) Max pick up setting is 1200A. Maximum time delay is 1 sec for fault current of 3000A or more. What the answers seem to imply is that 1 second it the maximum delay from pick up setting to 3000A. Most GFR's I can think of on bolted pressure switch setups have a definitely time delay after pickup with max of 1 sec, so the time delay would be 1 sec at 1200A pickup. Electronic breakers with GF can have I^2T slope functions, and the knee point at pickup can be above 1 sec, but is always below 1 sec by 3000A. But this would allow for a timing at a 1200A pickup of 2 secs in many cases. Code only specifies that the time delay has to be 1 second or less at 3000A.

  16. #39
  17. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation
    Quote Originally Posted by Wanderer20001us View Post
    See NEC 230.95 (A) Max pick up setting is 1200A. Maximum time delay is 1 sec for fault current of 3000A or more. What the answers seem to imply is that 1 second it the maximum delay from pick up setting to 3000A. Most GFR's I can think of on bolted pressure switch setups have a definitely time delay after pickup with max of 1 sec, so the time delay would be 1 sec at 1200A pickup. Electronic breakers with GF can have I^2T slope functions, and the knee point at pickup can be above 1 sec, but is always below 1 sec by 3000A. But this would allow for a timing at a 1200A pickup of 2 secs in many cases. Code only specifies that the time delay has to be 1 second or less at 3000A.
    Thank you. I bet that is one that I have been missing and thinking I got it right. Much appreciated!!

Page 4 of 4 FirstFirst ... 234
Subscribe

Share this thread

Related Topics

  1. I recently passed my NETA Level III exam. Ask me anything!
    By veracon0700 in forum NETA Level 3 Exam
    Replies: 7
    Last Post: May 18, 2020, 04:36 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net