    What IEEE level cable terminations should be used?

    In a contaminated outdoor live front transformer, what IEEE level cable terminations should be used?

    1
    2
    3
    4

  2. #2
  3. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by kenner14 View Post
    In a contaminated outdoor live front transformer, what IEEE level cable terminations should be used?

    1
    2
    3
    4
    Here may be a few things to help you out. Cable classes fall under IEEE 48. Unfortunately I do not have access to that standard without paying $150. But I found this information from 3M.

    Since I am not a cable splicer, my initial guess would be Class 1. But take a look for yourself.

    Class 1 Termination
    Provides electric stress control for the cable insulation shield
    terminus; provides complete external leakage insulation
    between the cable conductor(s) and ground; and provides a
    seal to the end of the cable against the entrance of the external
    environment and maintains the operating design pressure, if
    any, of the cable system. This class is divided into three types:
    Class 1A: For use on extruded dielectric cable
    Class 1B: For use on laminated dielectric cable
    Class 1C: Expressly for pressure-type cable systems

    Class 2 Termination
    Provides electric stress control for the cable insulation shield
    terminus, and provides complete external leakage insulation
    between the cable conductor(s) and ground.

    Class 3 Termination
    Provides electric stress control for the cable insulation shield
    terminus.

    Indoor Termination–Dry
    A termination intended for use where it is protected from
    solar radiation and precipitation and not subject to periodic
    condensation, or other excessive humidity (90% RH or more).
    May be installed in air conditioned or heated areas.

    Indoor Termination–Wet
    A termination intended for use where it is protected from
    direct exposure to both solar radiation and precipitation, but is
    subjected to climatic conditions that can cause condensation
    onto the termination surfaces.

    Outdoor Termination
    A termination intended for use where it is not protected from
    direct exposure to either solar radiation or precipitation. These
    are Class 1A, 1B, or 1C terminations. Class 2 terminations may
    also qualify.

Subscribe

Share this thread

Related Topics

  1. Field Testing of Motors, IEEE 43
    By SecondGen in forum NETA Level 3 Exam
    Replies: 8
    Last Post: December 24, 2021, 03:47 PM
  2. Cable hi-pot withstanding time, why 15 minutes?
    By moon1958moon in forum Electrical Testing Talk
    Replies: 31
    Last Post: April 16, 2019, 06:37 PM
  3. Replies: 2
    Last Post: July 5, 2018, 04:35 PM
  4. Cable fault locating questions
    By adamwilson in forum NETA Level 3 Exam
    Replies: 4
    Last Post: October 25, 2016, 03:18 PM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net