    How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    TTR standard deviation

    The standard deviation as defined by ANSI/IEEE C57.12.00-2006, Section 9.1 states that results should be within 0.5% of nameplate markings, with rated voltage applied to one winding. The TTR with accuracy of 0.1% is accepted as a referee.

    - Power Equipment Maintenance and Testing, Paul Gill


    ANSI/NETA standards also state that TTR results should be within 0.5%

  4. #3
  5. Join Date
    Jun 2016
    Posts
    28
    Reputation

    TTR

    Quote Originally Posted by shamimkhan View Post
    How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.
    In the NETA-MTS and ATS under electrical test results it says, "Turns-ratio test results should not deviate more than one-half percent from either the adjacent coils or the calculated ratio." Page 32 for both books.

Subscribe

Share this thread

Related Topics

  1. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Replies: 23
    Last Post: February 14, 2022, 10:36 AM
  2. Saturation test of a 1500/5 multi-ratio CT
    By Tseppish in forum Electrical Testing Talk
    Replies: 11
    Last Post: August 4, 2021, 10:21 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net