How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.
How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.
The standard deviation as defined by ANSI/IEEE C57.12.00-2006, Section 9.1 states that results should be within 0.5% of nameplate markings, with rated voltage applied to one winding. The TTR with accuracy of 0.1% is accepted as a referee.
- Power Equipment Maintenance and Testing, Paul Gill
ANSI/NETA standards also state that TTR results should be within 0.5%