    Vacuum Circuit Breaker

    What shall be the accepted value of contact resistance for Vacuum Circuit Breaker (11KV) ?
    What shall be the accepted value of leakage current for VCB (11KV),applied voltage is 18 KV ?
    What shall be the accepted value of contact timing ( closing time & opening time) for a VCB (11KV) & what is acceptable limit of closing time & opening time (for the contact) between the phases?
    Please also quote the reference standards.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    1.) Compare bolted connection resistance values to values of similar connections. Investigate values which deviate from those of similar bolted connections by more than 50 percent of the lowest value.


    2.) If no evidence of distress or insulation failure is observed by the end of the total time of voltage application during the dielectric withstand test, the circuit breaker is considered to have passed the test.


    3.) For air circuit breakers, contact timing values shall be in accordance with manufacturer’s published data. NETA specs do not call for this test on vacuum.


    All standards are based off NETA Section 7.6.3 Circuit Breakers, Vacuum, Medium-Voltage.


    Quote Originally Posted by shamimkhan View Post
    What shall be the accepted value of contact resistance for Vacuum Circuit Breaker (11KV) ?
    What shall be the accepted value of leakage current for VCB (11KV),applied voltage is 18 KV ?
    What shall be the accepted value of contact timing ( closing time & opening time) for a VCB (11KV) & what is acceptable limit of closing time & opening time (for the contact) between the phases?
    Please also quote the reference standards.

Subscribe

Share this thread

Related Topics

  1. Draw out circuit breaker positions, how many?
    By Mjeelemco in forum NETA Level 2 Exam
    Replies: 9
    Last Post: December 12, 2020, 07:54 AM
  2. When should circuit breaker contacts be lubricated?
    By zofofg in forum NETA Level 2 Exam
    Replies: 7
    Last Post: December 21, 2018, 07:27 PM
  3. Identify this circuit breaker symbol
    By MAKI2016 in forum NETA Level 2 Exam
    Replies: 10
    Last Post: September 27, 2017, 08:33 AM
  4. Do you always pull circuit breaker arc chutes?
    By wrh9278 in forum Electrical Testing Talk
    Replies: 3
    Last Post: April 24, 2016, 12:50 PM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net