how to perform insulation resistance test on three phase transformer

    #1
  1. Join Date
    Dec 2017
    Posts
    5
    Reputation

    how to perform insulation resistance test on three phase transformer

    please describe step by step guide how to perform insulation resistance test on three phase 2000 kva transformer

  2. #2
  3. Join Date
    Feb 2018
    Location
    Manchester, MI
    Posts
    3
    Reputation

    3 Phase Xfmr Insulation Resistance

    Quote Originally Posted by mask12900 View Post
    please describe step by step guide how to perform insulation resistance test on three phase 2000 kva transformer
    The answer to your question can be as lengthy as you would like, but the essentials are that there are 3 tests to perform:. Primary to Secondary with the ground guarded, primary to ground with the secondary guarded and secondary to ground with the primary guarded. The use of the guard will apply if the transformer in question is a Delta-Wye, Wye-Delta or a Delta-Delta. The guard cannot be used with a Wye-Wye where the H0 and X0 are tied together. Tests are conducted at voltages that exceed the Insulation rating but not the manufacturers recommended maximum. Tests are typically held for 10 minutes with readings recorded every minute in order to calculate a polarization index.

Subscribe

Share this thread

Related Topics

  1. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 2
    Last Post: June 10, 2018, 12:52 PM
  2. 230kV Auto-Transformer (Insulation Resistance Test)
    By rizza_gay in forum Electrical Testing Talk
    Replies: 8
    Last Post: January 19, 2018, 11:27 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net