please describe step by step guide how to perform winding resistance test on three phase dry type transformer
please describe step by step guide how to perform winding resistance test on three phase dry type transformer
Using a Transformer Winding Resistance tester connect the current leads and Voltage leads across a winding(In a Wye connected transformer it will be A-N,B-N,C-N, for Delta it will be A-B,B-C,C-A) wait for unit to stabilise and record value.
Delta values should always be measured values x1.732.
To tag on to the 10%, I have always heard you shouldn't exceed 10% rated current. Also the Manual for the Vanguard TTR and Winding resistance sets have really good info for dry types with in accessible neutrals and other nonstandard configurations.
http://www.vanguard-instruments.com/download
Breeze through and check out the manuals they have, I learned a good bit from them
Xmfr manufacturers typically recommend that the current output
selected should not exceed about 10% of the rated winding current, because it will cause erroneous readings due to heating of the winding.
• Always choose the highest current output possible for the expected resistance
value.
• Typical ranges are 0.1-10 % of rated winding current
Here are some slides from RichmondCC:
http://engineering.richmondcc.edu/Co...nce%20Test.pdf
Here is the procedure from TestGuy.net for Winding Resistance Testing:
https://testguy.net/content/276-Tran...ting-Explained