    Correct test voltage for 5KV cable?

    • Codes and Standards
    34. In accordance with NETA and IEEE standards the correct maintenance test voltage (dc) for 5KV rated EPR 133% insulation level cable is?
    Your Answer: 14kV
    Correct Answer: 11kV
    Help: NETA-MTS 2015 TABLE 100.6.1


    Is this correct as per NETA/ATS 2017. The way I am reading the standard it should be 36kV dc. Is this correct?.

  2. #2
  3. Steviep is offline Junior Member Pro Subscriber
    Join Date
    May 2016
    Location
    Newark, DE
    Posts
    13
    Reputation
    Quote Originally Posted by lfmontoyas View Post
    • Codes and Standards
    34. In accordance with NETA and IEEE standards the correct maintenance test voltage (dc) for 5KV rated EPR 133% insulation level cable is?
    Your Answer: 14kV
    Correct Answer: 11kV
    Help: NETA-MTS 2015 TABLE 100.6.1


    Is this correct as per NETA/ATS 2017. The way I am reading the standard it should be 36kV dc. Is this correct?.
    The question is looking to a maintenance voltage not acceptance.

  4. #3
  5. lfmontoyas's Avatar
    lfmontoyas is offline Junior Member Pro Subscriber
    Join Date
    Aug 2017
    Posts
    7
    Reputation
    Quote Originally Posted by Steviep View Post
    The question is looking to a maintenance voltage not acceptance.
    I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.

  6. #4
  7. Steviep is offline Junior Member Pro Subscriber
    Join Date
    May 2016
    Location
    Newark, DE
    Posts
    13
    Reputation
    Quote Originally Posted by lfmontoyas View Post
    I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.
    You need to look at the NETA MTS table 100.6 which is the maintenance standards. The ATS is acceptance testing which will be a higher value to ensure reliability.

  8. #5
  9. lfmontoyas's Avatar
    lfmontoyas is offline Junior Member Pro Subscriber
    Join Date
    Aug 2017
    Posts
    7
    Reputation
    Quote Originally Posted by Steviep View Post
    You need to look at the NETA MTS table 100.6 which is the maintenance standards. The ATS is acceptance testing which will be a higher value to ensure reliability.
    Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.

  10. #6
  11. Steviep is offline Junior Member Pro Subscriber
    Join Date
    May 2016
    Location
    Newark, DE
    Posts
    13
    Reputation
    Quote Originally Posted by lfmontoyas View Post
    Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.
    Im like a walking code book idk what it is but yea Ive got a lot of these number memorized even before i started studying for my NETA exams. I take my 3 on Monday. Best of luck!

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    NETA MTS 2015 Table 100.6.1

    Quote Originally Posted by lfmontoyas View Post
    Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.
    Here is the table from 2015 MTS...

    Click image for larger version. 

Name:	neta-table-100-6-1.png 
Views:	28 
Size:	58.2 KB 
ID:	234

  14. #8
  15. Behab1's Avatar
    Behab1 is offline Junior Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    8
    Reputation
    Quote Originally Posted by lfmontoyas View Post
    I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.
    The year matters.

  16. #9
  17. Join Date
    Jan 2015
    Posts
    29
    Reputation
    Funny thing is in the field I never do dc for service age cable anymore, everything is vlf. It will still be on the test though.

  18. #10
  19. test11's Avatar
    test11 is offline
    There can be only one!
    Member
    Join Date
    Mar 2017
    Location
    A hotel near you
    Posts
    38
    Reputation
    Quote Originally Posted by chils15 View Post
    Funny thing is in the field I never do dc for service age cable anymore, everything is vlf. It will still be on the test though.
    There are some hold-out customers that still use DC. Mainly city utilities where politics make it difficult to change the specs. That being said, some old site engineers aren't convinced either. I test DC a couple times a year for new cable.

Subscribe

Share this thread

Related Topics

  1. Fall of Potential Test - Voltage/Resistance Rises Dramatically
    By BrickSalad in forum Electrical Testing Talk
    Replies: 12
    Last Post: August 18, 2021, 11:18 AM
  2. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk
    Replies: 6
    Last Post: March 18, 2018, 08:29 PM
  3. Regulated voltage for powering up test sets?
    By veracon0700 in forum Electrical Testing Talk
    Replies: 4
    Last Post: July 21, 2015, 06:35 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net