So for any sort of over current relay, the pick-up in secondary amps is the tap, so to find the primary amps you just multiply it by the CT ratio (in this case 100). so it would be 500 Amps primary.
To take this one step further, if you had an under or over voltage relay, the same principle would apply. Let's say the tap for an under voltage relay was set at 82V and the PT ratio was 14400:120. So the relay would pick-up at 82V secondary, which translates to 9840V primary.