suchagrrl
In case anyone else is looking for this, I contacted Megger. This was the reply I got.
There is more flexibility in the manner of lead hookup than is commonly supposed. In the absence of any other considerations, industry standard is minus (-) to circuitry, plus (+) to ground. (Various labelling conventions apply to different models of tester; some are designated “Lâ€, for “lineâ€, and “Eâ€, for “earthâ€.) This configuration baffles some operators, depending on familiarity with conventions employed in other types of testing. In most cases, it doesn’t matter; the same resistance reading will prevail if the leads are exchanged. However, it has been observed that certain types of exotic insulating materials (e.g., some ceramics) yield different readings depending on the test lead configuration. In such instances, it has been observed that the aforementioned configuration yields the lower of the two readings. This is the desired of the two readings because insulation testing is generally concerned with safety, maintenance, and troubleshooting, and therefore the worst case reading would be the one which yields the most relevant information. Adopting a standard procedure for lead hookup relieves the operator from having to establish a specific knowledge of every type of material to be encountered as to whether it exhibits this effect, and prevents the less-informative higher reading from being inadvertently accepted as the final test result.
Additionally, some authorities assert that the reverse hookup can cause small amounts of contaminants to be carried into the insulation with the leakage current, whereas the accepted configuration would have the opposite effect.
Stated more specifically, if testing wire or cable, the minus lead would go to conductor(s), the positive to ground, shield, armor, or conduit. In extreme cases like direct-buried single conductor, a ground rod can be driven into the soil in the vicinity of the test, and the positive lead connected to it. The additional resistance of the soil as the leakage current travels to the rod is irrelevant when compared to the resistance of the insulation. With motors, generators, and transformers, the negative lead is to windings, the positive to case. With electrical tools and other equipment, negative is to circuitry, positive to frame.
However, the operator has additional freedom to employ other hookup configurations. Just be careful to avoid inadvertent continuity tests when elements thought to be isolated are in fact connected. Be familiar with the basic wiring diagram of the test item. Remember, there is supposed to be an insulation barrier between the two elements to which the leads are connected. As an example, wire and cable can be tested hot-to-neutral or phase-to-phase, but don’t forget to disconnect at the other end of the circuit. Otherwise, it’s only a high-voltage continuity test, and the resultant “zero†reading will be misinterpreted as indicating faulty cable. Worse, if there is equipment left connected, you could end up sending a high voltage through its circuitry.
The operator is free to make a judicious choice whether to test the entire piece of equipment as a single test, or to sectionalize. As an example, hot and neutral conductors can be clipped together and tested to ground; similarly, with three phases. Or, each conductor can be tested separately, either to ground or between each other. The choice is largely the operator’s, but standard procedure is to do a complete test first, then proceed with sectionalized tests only if the first test resulted in an unsatisfactory reading. Remember, testing the entire piece of equipment at once yields a worst case result, because electrically, the insulation is only as good as its weakest point. If the entire piece tests “goodâ€, its individual elements will read even higher.
Finally, many models have a third terminal. This is a guard, not a ground, as operators sometimes misinterpret from the “G†designation. Connecting it to ground will only serve to short-circuit the test and give an invalid reading. Its actual purpose is to act as a shunt circuit to remove parallel leakage paths from the measurement. If the test item has more than one leakage path in parallel, one can be shunted around the measurement circuit by connecting it to the guard, leaving a more specific measurement of the other path. Therefore, the guard acts as an extra diagnostic tool to permit more depth and scope to analytical testing and troubleshooting. A reasonably thorough knowledge of the test item is required, but when employed, the guard can yield invaluable detail.
Please let us know if you have any additional questions.
Regards,
Brian
Brian Hammerschmidt
Applications Specialist
Megger
Valley Forge Corporate Center
2621 Van Buren Ave.
Norristown, Pennsylvania 19403-1007 USA.