![Quote](images/misc/quote_icon.png)
Kalbi_Rob
For those interested in where I found the requirement in the NSTM 300 appendix G:
300-g.3.2 BODY RESISTANCE. At the outset of any consideration of safety from electric shock, it is important
to recognize that the resistance of the human body cannot be relied upon to prevent a fatal shock from 115
volt or even lower voltage circuits. When the skin is dry, it has a high resistance where it makes contact with the
electrodes through which current enters and leaves the body. The resistance may be high enough in this case to
protect a person from fatal shock even if one hand touches a bare conductor on one side of a 115volt line while
the other hand (or a foot) touches a bare conductor on the other side of the line. This is an exceptional case.
Onboard a ship, it is far more likely that the skin will be wet with perspiration or salt water. The contact resistance falls when the skin is wet, and the body resistance, measured from electrode to electrode, is low. Tests made
by the National Institute of Standards and Technology show that the resistance of the human body may be as low
as 500 ohms under unfavorable conditions. In warm and moist Marine environments such as are encountered on
naval vessels, body resistance as low as 300 ohms could be experienced. If 0.1 ampere is enough to cause death,
and if the body resistance can be as low as 300 ohms, it follows immediately that circuits above 30 volts can be
fatal. All circuits, even if of only a few volts, are potentially dangerous in that they may give rise to currents that
are immediately fatal, or that keep a person from letting go and ultimately cause death if they are not rescued by
their shipmates, or that cause a person to jump and perhaps fall under conditions that will cause serious injury.
The resistance of the body itself cannot be relied upon to provide protection from shock.