Results 1 to 10 of 18
Time curves for Siemens ETU745 & 766
    Mar 2018
    We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.
    Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?
    Any help would be appreciated.
    Thanks
    Dave.
    Quote Originally Posted by Dave32 View Post
    Thanks
    Dave.
    For that trip unit, I think you need to download the Siemens Time Current Curve (TCC) Software. Once installed, you can fill out the breaker info and trip unit settings and it will generate the curve for you.
    http://w3.usa.siemens.com/powerdistr...-software.aspx
    You might find the software a bit difficult to use, its outdated and not designed very well. As for ground fault, if I remember correctly on that trip unit you need to change the ground fault sensing scheme to source ground when primary injection testing, this looks at current on the neutral sensor only.
    I'm having trouble finding the specific manual for you trip unit. Some models have a switch, others have a jumper that can only be changed by removing the trip unit.
  5. Kalbi_Rob's Avatar
    290
    Thanks
    Dave.
    This is the manual that answers your question, a little late, but good for anybody else:
    https://docs.natlswgr.com/docs/W1000570.pdf
  7. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Michigan
    What do you use to power up a ETU 776 trip unit out of the cubicle?
  9. Kalbi_Rob's Avatar
    290
    Quote Originally Posted by oarreola View Post
    If I remember right (its been years since I had to do this), you can supply 24Vdc to X8 terminals 3(+) and 4(-). That being said, you need to verify you have a true filtered dc power supply, or it can fry the ETU trip unit.
  11. oarreola's Avatar
    oarreola is offline
    NETA 2
    Michigan
    What would be the best way to filter the dc supply?
  13. Kalbi_Rob's Avatar
    290
    If your power supply has a DC regulator, it will have a pure DC output. If your using a power supply that uses a bridge rectifier with a capacitor, it could produce a ripple DC output. A ripple DC output can be used, but if the capacitor starts to fail, the ripple can become larger and damage sensitive DC equipment.
    Thus, you need to know what kind of power supply you have based on manufacturer drawings. If you don't know, then your better off using the Siemens secondary kit, or powering up the switchboard CPT which powers up the equipment DC power supply.
  15. SecondGen's Avatar
    Siemens Secondary Kit, would recommend renting if you don't need it often.
  17. oarreola's Avatar
    oarreola is offline
    NETA 2
    Michigan
    Thanks guys!
    California
    21
    ETU 745 Primary Injection
    I just performed primary injection testing on a WL type Siemens breaker with a ETU 745 trip unit.
    The only way that I know of to obtain the time current curve is with their (Siemens) curve plotting software, Easy TCC.
  1. Helpful tips for testing Siemens SB-EC trip units (SBS circuit breakers)
    Last Post: August 27, 2021, 06:25 AM
  2. LV Breaker time curves calculators
    By Dave32 in forum Electrical Testing Talk
    Last Post: February 4, 2020, 04:04 PM
  3. Siemens 7UM62 Siprotec Relay - Generator Protection
    By balugalou in forum P&C / Relay Testing Talk
    Last Post: October 31, 2017, 11:09 AM
  4. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Last Post: June 11, 2015, 06:52 PM