    I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.

  2. #12
  3. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Join Date
    Apr 2015
    Location
    Michigan
    Posts
    5
    Reputation
    Quote Originally Posted by AaronCBI View Post
    I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.
    Do you have a model number of that power supply, I’ve been trying to get a hold of a representative for a week now with no response.

  4. #13
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by AaronCBI View Post
    I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.
    Yes, that is what I was talking about with DC ripple voltage. Either you have to have a DC Voltage Regulator or a proper Capacitor to filter out the DC ripple to be a pure DC signal. Essentially, you are must completely remove the AC sine wave into a pure DC flat voltage.
    Siemens electronics is very sensitive, and can be damaged if the ripple is too large.

  6. #14
  7. Join Date
    Sep 2017
    Location
    California
    Posts
    21
    Reputation

    Part#

    Quote Originally Posted by oarreola View Post
    Do you have a model number of that power supply, I’ve been trying to get a hold of a representative for a week now with no response.
    6EP1332-5BA20

  8. #15
  9. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Join Date
    Apr 2015
    Location
    Michigan
    Posts
    5
    Reputation
    Quote Originally Posted by AaronCBI View Post
    6EP1332-5BA20
    Thanks

  10. #16
  11. Join Date
    Dec 2014
    Posts
    3
    Reputation

    scott

    Quote Originally Posted by Kalbi_Rob View Post
    This is the manual that answers your question, a little late, but good for anybody else:

    https://docs.natlswgr.com/docs/W1000570.pdf
    To disable the ground fault during primary injection testing common 3 phases on the line side, then run current through 2 phases on the load side.

  12. #17
  13. Join Date
    Dec 2014
    Posts
    3
    Reputation

    scott

    Quote Originally Posted by oarreola View Post
    What do you use to power up a ETU 776 trip unit out of the cubicle?
    look at the terminal block labeled x8 on the top of the breaker. The ETU 776 need 24v DC to power the trip unit.
    On the x8 terminal block, hook the hot lead 24v to port #3. Hook the neutral lead to port #4

  14. #18
  15. Join Date
    Jan 2018
    Posts
    5
    Reputation

    Alternative methods to disable GFP

    Quote Originally Posted by scottbouch View Post
    To disable the ground fault during primary injection testing common 3 phases on the line side, then run current through 2 phases on the load side.
    Install jumpers between contacts 9-10 to disable NGS
    Install jumpers between contacts 11-12 to disable GFP

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. Helpful tips for testing Siemens SB-EC trip units (SBS circuit breakers)
    By SecondGen in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 27, 2021, 06:25 AM
  2. LV Breaker time curves calculators
    By Dave32 in forum Electrical Testing Talk
    Replies: 2
    Last Post: February 4, 2020, 04:04 PM
  3. Siemens 7UM62 Siprotec Relay - Generator Protection
    By balugalou in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: October 31, 2017, 11:09 AM
  4. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net