Time curves for Siemens ETU745 & 766

 Jump to latest post
Page 1 of 2 12 LastLast
    #1
  1. Join Date
    Mar 2018
    Posts
    4
    Reputation

    Time curves for Siemens ETU745 & 766

    We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

    Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

    Any help would be appreciated.


    Thanks
    Dave.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Dave32 View Post
    We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

    Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

    Any help would be appreciated.


    Thanks
    Dave.
    For that trip unit, I think you need to download the Siemens Time Current Curve (TCC) Software. Once installed, you can fill out the breaker info and trip unit settings and it will generate the curve for you.

    http://w3.usa.siemens.com/powerdistr...-software.aspx

    You might find the software a bit difficult to use, its outdated and not designed very well. As for ground fault, if I remember correctly on that trip unit you need to change the ground fault sensing scheme to source ground when primary injection testing, this looks at current on the neutral sensor only.

    I'm having trouble finding the specific manual for you trip unit. Some models have a switch, others have a jumper that can only be changed by removing the trip unit.

    Click image for larger version. 

Name:	siemens-etu-ground-fault-sensing.png 
Views:	9 
Size:	76.9 KB 
ID:	236

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Dave32 View Post
    We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

    Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

    Any help would be appreciated.


    Thanks
    Dave.
    This is the manual that answers your question, a little late, but good for anybody else:

    https://docs.natlswgr.com/docs/W1000570.pdf

  6. #4
  7. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Join Date
    Apr 2015
    Location
    Michigan
    Posts
    5
    Reputation
    What do you use to power up a ETU 776 trip unit out of the cubicle?

  8. #5
  9. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by oarreola View Post
    What do you use to power up a ETU 776 trip unit out of the cubicle?
    If I remember right (its been years since I had to do this), you can supply 24Vdc to X8 terminals 3(+) and 4(-). That being said, you need to verify you have a true filtered dc power supply, or it can fry the ETU trip unit.

    Click image for larger version. 

Name:	Siemens WLL.png 
Views:	40 
Size:	122.1 KB 
ID:	389

  10. #6
  11. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Join Date
    Apr 2015
    Location
    Michigan
    Posts
    5
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    If I remember right (its been years since I had to do this), you can supply 24Vdc to X8 terminals 3(+) and 4(-). That being said, you need to verify you have a true filtered dc power supply, or it can fry the ETU trip unit.

    Click image for larger version. 

Name:	Siemens WLL.png 
Views:	40 
Size:	122.1 KB 
ID:	389
    What would be the best way to filter the dc supply?

  12. #7
  13. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by oarreola View Post
    What would be the best way to filter the dc supply?
    If your power supply has a DC regulator, it will have a pure DC output. If your using a power supply that uses a bridge rectifier with a capacitor, it could produce a ripple DC output. A ripple DC output can be used, but if the capacitor starts to fail, the ripple can become larger and damage sensitive DC equipment.

    Thus, you need to know what kind of power supply you have based on manufacturer drawings. If you don't know, then your better off using the Siemens secondary kit, or powering up the switchboard CPT which powers up the equipment DC power supply.

  14. #8
  15. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by oarreola View Post
    What do you use to power up a ETU 776 trip unit out of the cubicle?
    Siemens Secondary Kit, would recommend renting if you don't need it often.

  16. #9
  17. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Join Date
    Apr 2015
    Location
    Michigan
    Posts
    5
    Reputation
    Thanks guys!

  18. #10
  19. Join Date
    Sep 2017
    Location
    California
    Posts
    21
    Reputation

    ETU 745 Primary Injection

    I just performed primary injection testing on a WL type Siemens breaker with a ETU 745 trip unit.
    The only way that I know of to obtain the time current curve is with their (Siemens) curve plotting software, Easy TCC.

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Helpful tips for testing Siemens SB-EC trip units (SBS circuit breakers)
    By SecondGen in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 27, 2021, 06:25 AM
  2. LV Breaker time curves calculators
    By Dave32 in forum Electrical Testing Talk
    Replies: 2
    Last Post: February 4, 2020, 04:04 PM
  3. Siemens 7UM62 Siprotec Relay - Generator Protection
    By balugalou in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: October 31, 2017, 11:09 AM
  4. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM