EATON Magnum DS Switchgear – CT Shorting Block Design Flaw

    #1
  1. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    EATON Magnum DS Switchgear – CT Shorting Block Design Flaw

    Something to keep an eye out for if you come across EATON Magnum DS switchgear. The main circuit breaker shorting block is located in close proximity to grounded cubicle hardware, which can cause a short to develop in the CT secondary wiring circuit.

    Click image for larger version. 

Name:	magnum-ds-shorting-block-1.jpg 
Views:	9 
Size:	401.0 KB 
ID:	238

    Long story short, this issue was discovered when attempting to megger the CT secondary wiring during acceptance testing. After lifting the known single ground, continuity tests revealed a short remaining somewhere in the circuit.

    This was obviously unexpected as there should only be a single ground. It took about 15 minutes to narrow the problem down to the shorting block, which was was lifted from where it was mounted and tested fine.

    Once put back in place, the short returned. At first it was thought that the block insulation was defective, but after a close visual inspection it was noticed that the shorting pins were making slight contact with an adjacent mounting screw.

    Click image for larger version. 

Name:	magnum-ds-shorting-block-2.jpg 
Views:	5 
Size:	336.3 KB 
ID:	239

    Short.

    Click image for larger version. 

Name:	magnum-ds-shorting-block-3.jpg 
Views:	2 
Size:	334.3 KB 
ID:	240

    No Short.

    As a temporary fix, electrical tape was put over the screw to give some insulation. It was recommended that the contractor swap the position of the two blocks.

    Click image for larger version. 

Name:	magnum-ds-shorting-block-4.jpg 
Views:	2 
Size:	330.3 KB 
ID:	241

    Photos were taken once everything was back together, ground was lifted during the test.

Subscribe

Share this thread

Related Topics

  1. Shorting transformer windings for PI, why is it done?
    By SecondGen in forum Electrical Testing Talk
    Replies: 29
    Last Post: November 12, 2020, 08:15 AM
  2. Gas Insulated Switchgear
    By jflan13 in forum Electrical Testing Talk
    Replies: 6
    Last Post: January 27, 2018, 12:20 PM
  3. EATON PX2000 Meter: How to Change IP Address in Power Xpert
    By SecondGen in forum Technical Documents
    Replies: 1
    Last Post: September 29, 2016, 05:07 PM
  4. EATON Magnum DS tripping free? Give this mechanism spring a check.
    By SecondGen in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 28, 2016, 06:33 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net