Transformer Exam Questions, NETA Level 2

    #1
  1. Join Date
    May 2017
    Posts
    6
    Reputation

    Transformer Exam Questions, NETA Level 2

    Can someone help me with these two questions:

    What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kva, 7.0% impedance transformer?

    A given 1000kva wye-wye transformer has a phase voltage of 277; what would you expect the full load line current to measure?

  2. #2
  3. Join Date
    Jun 2015
    Posts
    25
    Reputation
    Quote Originally Posted by adamstraub View Post
    Can someone help me with these two questions:

    What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kva, 7.0% impedance transformer?

    A given 1000kva wye-wye transformer has a phase voltage of 277; what would you expect the full load line current to measure?
    i got the 1st question on my practice exam, and got it wrong also. waiting for answer too.....

  4. #3
  5. Join Date
    Jan 2019
    Posts
    1
    Reputation
    Quote Originally Posted by adamstraub View Post
    Can someone help me with these two questions:

    What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kva, 7.0% impedance transformer?

    A given 1000kva wye-wye transformer has a phase voltage of 277; what would you expect the full load line current to measure?
    This quick calculation can help you determine the fault current on the secondary of a transformer for the purpose of selecting the correct overcurrent protective devices that can interrupt the available fault current.

    Fault Current = Full Load Amps / % Impedance (Z)

    Example: Calculate the maximum fault current for a transformer rated 13.8kV-480Y/277V 1000kVA 5.75%Z


    Step 1: Determine Full Load Amps (FLA)

    You can determine the Full Load Amps of a transformer with the following formula: FLA = VA / L-L Voltage x 1.732, so using the example above we get FLA = 1000000 / 480 x 1.732 or 1000000 / 831.36 = 1202.84 (note the conversion from kVA to VA, 1000 x 1000 = 1000000).

    FLA = 1203 amperes


    Step 2: Divide FLA by Impedance
    The next step is to simply divide the number obtained in step 1 by the transformer nameplate impedance. Using the example above we get: 1203 / 0.0575 = 20921.73 (REMEMBER TO CONVERT PERCENT TO DECIMAL, if 100% = 1.00 then 5.75% = 0.0575).

    FC = 20,922 amperes


    If a main breaker was to be installed in the circuit on the secondary of the transformer used in this example, it would have to have an Interrupting Rating greater than 21,000A.

Subscribe

Share this thread

Related Topics

  1. NETA 4 Exam Questions 7/2018
    By MartyCoyne in forum NETA Level 4 Exam
    Replies: 29
    Last Post: June 22, 2022, 10:46 PM
  2. NETA 4 exam questions I am unsure about
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 2
    Last Post: August 6, 2021, 07:15 AM
  3. Why so few questions for NETA 4 exam?
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 3
    Last Post: February 10, 2020, 12:14 PM
  4. Neta 3 Exam pointers and questions
    By Zepold72 in forum NETA Level 3 Exam
    Replies: 13
    Last Post: April 29, 2016, 05:25 PM
  5. Official NETA Level 2 Exam Most Missed Questions, Spring 2000
    By SecondGen in forum NETA Level 2 Exam
    Replies: 6
    Last Post: March 16, 2016, 08:18 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net