Rating plug removal prior to dielectric testing

 Jump to latest post
    #1
  1. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    Rating plug removal prior to dielectric testing

    When dielectric testing power circuit breakers, specifically Square D w/ Micrologic, we sometimes may need to pull the rating plug to avoid damaging the trip unit.

    My question to the community is this: do you pull the plug before or after your trip test? I've been doing megger first and then trip testing because my concern is that after pulling the plug how do I know the trip unit will function?

    Sure, i could run another quick trip test but I want to avoid extra steps. The probability of something going wrong is low I'm sure but I was mainly looking to get some opinions from others on how they test.

    Click image for larger version. 

Name:	rating-plug-warning.jpg 
Views:	88 
Size:	44.5 KB 
ID:	260

  2. #2
  3. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by SecondGen View Post
    When dielectric testing power circuit breakers, specifically Square D w/ Micrologic, we sometimes may need to pull the rating plug to avoid damaging the trip unit.

    My question to the community is this: do you pull the plug before or after your trip test? I've been doing megger first and then trip testing because my concern is that after pulling the plug how do I know the trip unit will function?

    Sure, i could run another quick trip test but I want to avoid extra steps. The probability of something going wrong is low I'm sure but I was mainly looking to get some opinions from others on how they test.

    Click image for larger version. 

Name:	rating-plug-warning.jpg 
Views:	88 
Size:	44.5 KB 
ID:	260
    I operate the same as you. The last thing I want to be certain of is that the trip unit works.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by SecondGen View Post
    When dielectric testing power circuit breakers, specifically Square D w/ Micrologic, we sometimes may need to pull the rating plug to avoid damaging the trip unit.

    My question to the community is this: do you pull the plug before or after your trip test? I've been doing megger first and then trip testing because my concern is that after pulling the plug how do I know the trip unit will function?

    Sure, i could run another quick trip test but I want to avoid extra steps. The probability of something going wrong is low I'm sure but I was mainly looking to get some opinions from others on how they test.

    Click image for larger version. 

Name:	rating-plug-warning.jpg 
Views:	88 
Size:	44.5 KB 
ID:	260
    I worked with an individual years ago that refused to test a breaker until he performed insulation resistance test first. We tested a breaker and found out it failed on insulation resistance after some difficult set up to perform the trip tests. So, it rubbed off on me and I've adopted it as a norm. It makes sense because if the breaker fails resistance testing, then it spares me having to set up to perform trip test on a failed breaker. It never occurred to me to worry about the rating plug since we test in that order.
    That being said, I have seen numerous people bend the pins on the Micrologic rating plugs when performing this test also. This helps to identify when this happens.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    I worked with an individual years ago that refused to test a breaker until he performed insulation resistance test first. We tested a breaker and found out it failed on insulation resistance after some difficult set up to perform the trip tests. So, it rubbed off on me and I've adopted it as a norm. It makes sense because if the breaker fails resistance testing, then it spares me having to set up to perform trip test on a failed breaker. It never occurred to me to worry about the rating plug since we test in that order.
    That being said, I have seen numerous people bend the pins on the Micrologic rating plugs when performing this test also. This helps to identify when this happens.

    The theory makes sense. We usually megger last to be sure the breaker is clear before putting it in the cell, this also allows the insulation and contacts to heat up during trip testing.

    I'd imagine a line to load megger test wouldn't affect anything in this case, only phase to phase? If so it would make sense to megger, trip test, ducter, and megger open again as a final safety check.

Subscribe

Share this thread

Related Topics

  1. Testing Solid Dielectric Cable
    By CosmoVA in forum Electrical Testing Talk
    Replies: 6
    Last Post: May 25, 2018, 06:12 AM
  2. Continuous current rating of a circuit breaker
    By mainmanmerc in forum NETA Level 2 Exam
    Replies: 4
    Last Post: October 22, 2016, 07:32 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net