I need your help. Which Circuit Breakers Should Have Test according to NETA ? I mean sometimes there are a lot of little circuit breakers in Panelboards etc 20A. Should we test them also ?
Thanks for help
Hi guys,
I need your help. Which Circuit Breakers Should Have Test according to NETA ? I mean sometimes there are a lot of little circuit breakers in Panelboards etc 20A. Should we test them also ?
Thanks for help
This is for acceptance testing by the way, I've also seen specs that call for "main breakers" only. For maintenance we usually secondary inject unless the customer requests primary, same 400A and above rule usually applies if customer has no idea what they want to test. Which application is this?
NETA ATS and MTS both state that the owner/user is responsible for deciding which equipment to test.
ATS 4.1.4
MTS 4.1.3