4/0 grounded cable is rated at 43kA for 15cycles. What is the minimum number of cables per phase required to safely ground a 2500kVA 5.75%Z transformer on the 480V side?
A-1
B-2
C-3
D-4
Looking for help on this. XFMR fault current is 52,297 on the 480V side assuming 3phase? my guess is 2 cables per phase.
480*1.732 = 831.36
2500000 / 831.36 = 3007.12
3007.12 / 0.0575 = 52297