GE Protection Setting Help

    #1
  1. Join Date
    Aug 2018
    Posts
    1
    Reputation

    GE Protection Setting Help

    hi, anybody with ge protection?
    I am questioning the signal source 2 setting. We are using source 2 for loss of excitation but the the source 2 setting has vt phase set at "none". will the loss of excitation function eventhough the setting of the source 2 vt phase is set at none?

  2. #2
  3. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by jomawi View Post
    hi, anybody with ge protection?
    I am questioning the signal source 2 setting. We are using source 2 for loss of excitation but the the source 2 setting has vt phase set at "none". will the loss of excitation function eventhough the setting of the source 2 vt phase is set at none?
    To be honest, I'm not sure! But the only way to find out would be to take the generator offline and test the relay with the as found settings. If its not possible to take the generator offline, acquire another relay and case, and upload the settings from the in service generator. Then you should be able to perform your relay testing to verify whether or not that function is working properly. If it isn't working on the "test" relay, then you can be certain it isn't working on the one in service.

    Also I am not sure of the relay. Are you referring to a G60?

    Sorry I can't give you a direct answer.

  4. #3
  5. JohnnyH is offline Junior Member
    Join Date
    Nov 2018
    Location
    California
    Posts
    1
    Reputation
    Quote Originally Posted by jomawi View Post
    hi, anybody with ge protection?
    I am questioning the signal source 2 setting. We are using source 2 for loss of excitation but the the source 2 setting has vt phase set at "none". will the loss of excitation function eventhough the setting of the source 2 vt phase is set at none?
    I had the same issue with two GE F60’s except it was the ground ct signal source that was set to none. When I tested it, the ground fault protection would not operate. Once we selected a signal source it operated as expected. I would bet money that the loss of exitation element will not work until you select a signal source for it.

Subscribe

Share this thread

Related Topics

  1. Ground fault trips at half of setting
    By joenavymctest in forum P&C / Relay Testing Talk
    Replies: 6
    Last Post: March 6, 2020, 08:45 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net