VLF vs AC HiPot

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. davidantkowiak is offline Junior Member Pro Subscriber
    Join Date
    Jul 2017
    Posts
    1
    Reputation

    Vlf

    Quote Originally Posted by ElectricalTestTech View Post
    So as a brief answer, yes, I have used a VLF to hi pot a breaker in a bind. Just like you, it was all I had on site. In my eyes, a VLF was better than just a 5kV megger and DLRO. What I will speak on is "stress"... Think about why we use VLF on cables. We use it because using an AC hi pot at 60Hz is very stressful and damaging to cables (it's more technical than that explanation, but being brief). In my mind, I want to stress this breaker and make sure it won't fail on me when I rack it back into an energized cubicle. I want to stress it to make sure it wont fail when I close it and energize a circuit. That is the way I think of this topic. Its one of those statements that you make, "use the proper tool for the job" kind of deals. Use what's available to you, because something is always better than nothing

    Rc=1/6.28*F*C the only variable in cable reactance is f. The reasoning behind vlf is that the equipment would be less portable at higher frequency due to Rc. When testing a vacuum bottle the bottle would only be exposed to test voltage at .1 hz so you would have to test for a longer period to obtain sustained voltage at time period.

  2. #12
  3. BrickSalad is offline Junior Member Pro Subscriber
    Join Date
    Oct 2015
    Posts
    11
    Reputation
    Quote Originally Posted by davidantkowiak View Post
    Rc=1/6.28*F*C the only variable in cable reactance is f. The reasoning behind vlf is that the equipment would be less portable at higher frequency due to Rc. When testing a vacuum bottle the bottle would only be exposed to test voltage at .1 hz so you would have to test for a longer period to obtain sustained voltage at time period.
    Like you, I have also heard that the main reason behind VLF over AC hipot is equipment portability. However, it's also true that frequency does effect stress. Specifically, higher frequencies correspond to lower breakdown voltages.

    I'm not sure if this applies to a vacuum bottle though. The reasons I've read for why high voltage causes more stress on insulation is heat and partial discharge, which wouldn't really effect empty space.

  4. #13
  5. Join Date
    Jan 2019
    Posts
    19
    Reputation

    "AC Hipot damaging to cables..."

    Quote Originally Posted by ElectricalTestTech View Post
    So as a brief answer, yes, I have used a VLF to hi pot a breaker in a bind. Just like you, it was all I had on site. In my eyes, a VLF was better than just a 5kV megger and DLRO. What I will speak on is "stress"... Think about why we use VLF on cables. We use it because using an AC hi pot at 60Hz is very stressful and damaging to cables (it's more technical than that explanation, but being brief). In my mind, I want to stress this breaker and make sure it won't fail on me when I rack it back into an energized cubicle. I want to stress it to make sure it wont fail when I close it and energize a circuit. That is the way I think of this topic. Its one of those statements that you make, "use the proper tool for the job" kind of deals. Use what's available to you, because something is always better than nothing
    Just wanted to touch on your reasoning behind not using a power freq test set (AC Hipot) vs using a VLF.

    60Hz will not damage insulation. AC testing is by its nature not destructive to cable insulation. DC testing can reduce cable life of service aged cables by causing/propagating water trees that may not have otherwise been an issue. A 30-60 minute VLF will find damaged insulation and potentially cause a flash over, but generally only in cable that was already defective. Its lifespan is. Ot reduced by the VLF like it is in a DC test.

    However, due to the capacitive reactance of MV cable, 60hz test sets are just not feasible in the field. Increases in frequency. Since the dielectric (insulation) is not fully charged with each cycle, leakage and charging current would be pretty high at 60hz. The power output of a test set that can reach 60kV along with these high levels of current would prohibit field use.

    Since DC will charge and stabilize, current requirements and VA will be lower. Since DC is destructive, we use a VLF which allows us to test very capacitive devices (cable) without needing a trailer sized test set. VLF gives us the best of both worlds.

    In an ideal world we would test cables at power frequency.

  6. #14
  7. NBatson's Avatar
    NBatson is offline
    I NETA BREAK
    Junior Member
    Join Date
    Feb 2019
    Location
    TX Gulf Coast
    Posts
    19
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    So, recently went onto a job to perform VLF testing of 2 sets of 35kV cables, when the customer threw a curve ball at me to test the 35kV breakers. I had no ac hipot to perform vacuum bottle integrity and withstand test. Our management does not want us to test with DC on vacuum bottles, as there is documentation that dc can damage vacuum bottles (haven't personally seen this documentation other than production of X-Ray radiation), so would VLF be sufficient as a AC hipot test on Vacuum bottle and withstand test for breakers?

    Per manufacturer 60kVAC or 82kVDC is required to perform vacuum bottle integrity on 35kV breaker. HV60 only puts out 60kVDC or 44kVAC but NETA allows for 42kVAC for testing breakers. I'm more interested in hearing the community discussion of using the VLF for AC HiPot for or against arguments.

    Did you ever find anything on this? We recently acquired a line up of ABB Advac 15kv breakers. The IL wants VLF testing done on the vacuum bottles. This is the first we have done like this but has brought up using VLF for vacuum contactors. Our VLF test sets weighs a fraction of what our AC hipot weighs.

    Our AB vacuum contact says it’s a viable test and directly comparable to AC hipot??

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. Should I HIPOT before or after other tests?
    By DJ-Jokes in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 3, 2021, 02:10 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net