GE Burlington continues to strongly recommend the use of an AC high potential machine for vacuum interrupter integrity tests. DC testing of vacuum interrupters should only be utilized if an AC tester is not available, and should be used for quick field checks only.
Our experience with DC testers over many years indicates they frequently yield false negative test results, due partially to the capacitive component of the vacuum interrupter during DC testing, and to the fact that most lightweight DC testers have a very low leakage current trip setting. They will however, reliably indicate a truly failed bottle if the voltage output is set at 50kV DC.
If using a DC tester, and a test indicates a bad interrupter, retest with the polarity of the DC test voltage reversed. If this results again in a failure, we would recommend a final AC test prior to contacting GE Post Sales Service or discarding the interrupter.
No attempt should be made to try and compare the condition of one vacuum interrupter with another, or to correlate the condition of any interrupter to low values of DC leakage current. There is no significant correlation.
After the high potential voltage is removed, discharge any electrical charge that may be retained.
CAUTION: MANY OLDER DC HIGH POTENTIAL MACHINES ARE HALFWAVE RECTIFIERS. THIS TYPE OF HI-POT TESTER MUST NOT BE USED TO TEST VACUUM INTERRUPTERS. THE CAPACITANCE OF THE POWER/VAC BOTTLE IS VERY LOW AND THE LEAKAGE IN THE RECTIFIER AND ITS DC VOLTAGE MEASURING EQUIPMENT IS SUCH THAT THE PULSE FROM THE HALF-WAVE RECTIFIER MAY ACTUALLY BE IN THE NEIGHBORHOOD OF 120KV, WHEN THE METER IS ONLY READING 40KV.
IN THIS CASE, SOME PERFECTLY GOOD BOTTLES CAN SHOW A RELATIVELY HIGH LEAKAGE CURRENT SINCE IT IS THE PEAK VOLTAGE OF 120KV THAT IS PRODUCING ERRONEOUS BOTTLE LEAKAGE CURRENT. IN ADDITION, THE X - RADIATION WILL BE OF CONCERN.