Fluke 1750 PQM data loss after utility switching operations

    #1
  1. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    Fluke 1750 PQM data loss after utility switching operations

    Data from a 30-day power quality recording was completely wiped out after the utility company de-energized the feeder being monitored, causing a flood of events.

    This was a dual source 15kV switchgear that was being evaluated for 90 days because the gear was to be completely replaced. A Fluke 1750 recording meter had been set up on the secondary circuits inside both of the main breaker cubicles for weeks prior to utility operations.

    This is a customer owned switchgear but the utility company has access to a switchyard just behind the substation and also the main breakers in the 15kV switchgear. PQM voltage probes were connected to the secondary of the PT and current at the protective relays.

    When I came in for a routine checkup of the meter (now 3 weeks into recording), I noticed one of the breakers was racked out. At first I didn’t think it would be a big deal but once I got into things it was a shock to see I only two days’ worth of data.

    To make a long story short, by pulling the PT drawer, the PQM recognized a loss of voltage and started to log events. After about 5 days of recording nothing but events, it appears that the memory had reached capacity and older data from weeks ago was being overwritten to make space for new data.

    Under normal circumstances, opening and removing the main breaker would not affect the recording meter as line bus voltage would still be present (unless the feeder was de-energized). It would be expected to see current drop off when the breaker was opened.

    However, since the PT drawer was also racked out, voltage sensed by the recording meter was lost as the meter was connected to the secondary side of the PT to monitor voltage levels that exceed the rating of the unit. This caused a loss of line voltage condition on the meter, triggering events.

    Needless to say the recorded data for the weeks prior to my arrival was wiped from the memory, leaving me with nearly 20,000 events and no usable data over the course of only a couple days. It’s still unclear why the feeder was taken out (could have been emergency) but had we been notified the data could have been downloaded before having a chance to overwrite.

  2. #2
  3. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by SecondGen View Post
    Data from a 30-day power quality recording was completely wiped out after the utility company de-energized the feeder being monitored, causing a flood of events.

    This was a dual source 15kV switchgear that was being evaluated for 90 days because the gear was to be completely replaced. A Fluke 1750 recording meter had been set up on the secondary circuits inside both of the main breaker cubicles for weeks prior to utility operations.

    This is a customer owned switchgear but the utility company has access to a switchyard just behind the substation and also the main breakers in the 15kV switchgear. PQM voltage probes were connected to the secondary of the PT and current at the protective relays.

    When I came in for a routine checkup of the meter (now 3 weeks into recording), I noticed one of the breakers was racked out. At first I didn’t think it would be a big deal but once I got into things it was a shock to see I only two days’ worth of data.

    To make a long story short, by pulling the PT drawer, the PQM recognized a loss of voltage and started to log events. After about 5 days of recording nothing but events, it appears that the memory had reached capacity and older data from weeks ago was being overwritten to make space for new data.

    Under normal circumstances, opening and removing the main breaker would not affect the recording meter as line bus voltage would still be present (unless the feeder was de-energized). It would be expected to see current drop off when the breaker was opened.

    However, since the PT drawer was also racked out, voltage sensed by the recording meter was lost as the meter was connected to the secondary side of the PT to monitor voltage levels that exceed the rating of the unit. This caused a loss of line voltage condition on the meter, triggering events.

    Needless to say the recorded data for the weeks prior to my arrival was wiped from the memory, leaving me with nearly 20,000 events and no usable data over the course of only a couple days. It’s still unclear why the feeder was taken out (could have been emergency) but had we been notified the data could have been downloaded before having a chance to overwrite.

    Very interesting. We install meters to collect data. We spend time thinking about routing extension cords out of the way to avoid being inplugged. We come up with clever ways of duct taping cords to be plugged into receptacles, or tie-wrapping them to receptacles.

    We come up with ways of keeping the temporary installation electrically safe, to those who may wander into the electrical room. All of this thought goes into signage and installation that I never thought about putting signage on the breaker being monitored to call my cell if the circuit is to be de-energized.

    Thanks for making me aware of another scenario to look out for.

Subscribe

Share this thread

Related Topics

  1. Breathing patterns when performing hot work and switching
    By electrolyte in forum Safety and Arc Flash Talk
    Replies: 4
    Last Post: March 19, 2022, 12:36 PM
  2. Replies: 4
    Last Post: October 31, 2021, 06:02 AM
  3. Have you ever used a Fluke 1750 power analyzer?
    By NWILLJR1020 in forum Electrical Testing Talk
    Replies: 2
    Last Post: November 21, 2017, 06:09 AM
  4. Partial Discharge Data Interpretation
    By ies0900012 in forum Electrical Testing Talk
    Replies: 2
    Last Post: July 21, 2016, 06:27 PM
  5. Looking for data sheets for 40 year old Sq D equipment
    By John B in forum Technical Documents
    Replies: 2
    Last Post: November 3, 2014, 08:48 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net