Received a Pair of similar questions involving current calculations on Transformers, but I'm having trouble figuring out their math.
A primary injection is to be performed on a transformer rated 138kV/25kV, 2500kVA, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?
a) 18.116A
b) 12.5A
c) 226.45A
d) 0.787A
e) 1.36A
And:
A primary injection is to be performed on a D-Y transformer rated 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?
a) 0.262A
b) 0.455A
c) 0.787A
d) 1.36A