Ground Impedance Testing

    #1
  1. Join Date
    Aug 2018
    Posts
    6
    Reputation

    Ground Impedance Testing

    Hello - Our company purchased recently Omicron test set for us to perform Ground grid assessment, line impedance and Step and Touch. We have really only just begun the full capability of the test set, which works very nicely but had questions on Point to Point values and what is acceptable...I believe within a Substation of 115kv size, the ground impedance may only be required to be no more than 5 ohms, but I am not directly measuring the ground I am measuring from my reference point to another known point within our sub (Breaker GND, Switch GND and so forth). So what is actually permissible? We measured .5 milli ohms on average with injecting 100 amps, mind that the Sub is approx 300'X900'. I appreciate any comments regarding this Post. Thanks

  2. #2
  3. Join Date
    Dec 2015
    Posts
    38
    Reputation
    Quote Originally Posted by africanamber View Post
    Hello - Our company purchased recently Omicron test set for us to perform Ground grid assessment, line impedance and Step and Touch. We have really only just begun the full capability of the test set, which works very nicely but had questions on Point to Point values and what is acceptable...I believe within a Substation of 115kv size, the ground impedance may only be required to be no more than 5 ohms, but I am not directly measuring the ground I am measuring from my reference point to another known point within our sub (Breaker GND, Switch GND and so forth). So what is actually permissible? We measured .5 milli ohms on average with injecting 100 amps, mind that the Sub is approx 300'X900'. I appreciate any comments regarding this Post. Thanks
    From what I can tell you are using the set for point-to-point DLRO at 100A to verify continuity between equipment. Average values of 0.5 milliohms (500 microhms) are good numbers in my opinion. Depending on the distance between equipment higher readings may still be acceptable.

  4. #3
  5. Join Date
    Aug 2018
    Posts
    6
    Reputation

    Thanks

    Quote Originally Posted by Sanjayo View Post
    From what I can tell you are using the set for point-to-point DLRO at 100A to verify continuity between equipment. Average values of 0.5 milliohms (500 microhms) are good numbers in my opinion. Depending on the distance between equipment higher readings may still be acceptable.
    Thank you Sanjayo. I appreciate your input.

Subscribe

Share this thread

Related Topics

  1. Looking for chart on soil types for ground resistance testing
    By madMAX in forum Technical Documents
    Replies: 7
    Last Post: June 27, 2018, 12:49 PM
  2. Ground Resistance Testing IT System
    By rig-electrician in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 13, 2017, 07:56 AM
  3. Testing ground resistance with no earth to drive rods
    By iwanttotest in forum Electrical Testing Talk
    Replies: 2
    Last Post: February 23, 2017, 09:39 AM
  4. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 02:46 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net