Most common rated insulation for control wiring

 Jump to latest post
    #1
  1. E-DivMafia is offline Junior Member Pro Subscriber
    Join Date
    Feb 2018
    Posts
    5
    Reputation

    Most common rated insulation for control wiring

    Which is the most common rated insulation for control wiring?

  2. #2
  3. RickYoungblood is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    3
    Reputation
    Quote Originally Posted by E-DivMafia View Post
    Which is the most common rated insulation for control wiring?
    It’s 600V. That’s the common insulation class for panel wire

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by E-DivMafia View Post
    Which is the most common rated insulation for control wiring?
    When I hear control wiring I think switchgear, which is normally 600V rated SIS wire.

  6. #4
  7. Join Date
    Dec 2018
    Location
    Atlanta, GA
    Posts
    27
    Reputation
    Quote Originally Posted by RickYoungblood View Post
    It’s 600V. That’s the common insulation class for panel wire
    Is there a table or something where these values can be looked up?

  8. #5
  9. E-DivMafia is offline Junior Member Pro Subscriber
    Join Date
    Feb 2018
    Posts
    5
    Reputation
    Quote Originally Posted by Ronwilson1801 View Post
    Is there a table or something where these values can be looked up?
    I am not aware of one, but would be interested to know as well.

  10. #6
  11. Join Date
    Apr 2018
    Location
    Michigan
    Posts
    40
    Reputation
    Quote Originally Posted by E-DivMafia View Post
    I am not aware of one, but would be interested to know as well.
    NEC Table 310.104(A) provides application and insulation ratings for 600V class wire.
    NEC Table 310.15(B)(16) provides ampacities.

    SIS (insulation rating 90C) is what I would first think to use in most switchgear control wiring applications, but it can vary based on actual need in a substation or switchgear.

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by E-DivMafia View Post
    I am not aware of one, but would be interested to know as well.
    Here is a PDF with various tables from NEC Article 310, might be worth a look: https://www.houwire.com/pdf/Article_...ral_Wiring.pdf

Subscribe

Share this thread

Related Topics

  1. Can this CT produce enough voltage to trip a relay?
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 10
    Last Post: February 5, 2021, 10:28 AM
  2. SF-6 gas analyzers, which is most common?
    By KBloomer in forum Electrical Testing Talk
    Replies: 3
    Last Post: January 29, 2020, 01:58 PM
  3. most common problem when testing microprocessor relays
    By sthrcave in forum NETA Level 3 Exam
    Replies: 1
    Last Post: May 31, 2019, 06:43 AM
  4. LTC Control Cabinet Test
    By ddyson7985 in forum Electrical Testing Talk
    Replies: 5
    Last Post: August 8, 2018, 06:36 PM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net