    Easy method for ground fault testing EATON 310 and 310+ trip units

    Ground fault testing circuit breakers equipped with G-Series 310 and 310+ can be a real pain if you are unfamiliar with the power requirements of these trip units. The factory procedure from EATON requires you to use two primary-injection test sets and convoluted test connections for a simple ground fault test, fortunately there is a better way.

    Click image for larger version. 

Name:	eaton-rg-frame-with-310-trip-unit.jpg 
Views:	118 
Size:	139.4 KB 
ID:	302

    You can use the EATON Functional Test Kit to provide the 310 and 310+ trip unit with adequate sensing power for a single pole ground fault test. Simply turn the dial on the test kit to "Power Up" and hold down the "Push to test" button during your primary injection test.

    Click image for larger version. 

Name:	eaton-digitrip-310-functional-test-kit.jpg 
Views:	13 
Size:	175.3 KB 
ID:	301

    I discovered this trick today while acceptance testing a 2500A switchboard main breaker (EATON RG Frame) with ground fault. I was unaware of the power requirements and tried to test the switchboard ground fault system as normal, with a single current box and a jumper.

    At first I was getting no trip and a solid green LED on the trip unit which should normally be a flashing green, indicating that the trip unit is working properly. I made a phone call to another tech who is familiar with these trip units and he forwarded me this crazy procedure from EATON.

    According to their procedure I needed two test sets. One to push enough current to power the trip unit through two poles in series, and a second test set to simulate the ground fault current through the free pole.

    Click image for larger version. 

Name:	eaton-310-ground-fault-test-connections.png 
Views:	12 
Size:	27.5 KB 
ID:	300

    This is just a ludicrous design in my opinion and I had no additional current sources, so I had to improvise. Luckily I had the functional test kit with me and remembered it has a power up function that gave me the flashing LED.

    Sure enough using one hand to hold the button and another to push current with my test set did the trick, I got the trip and no trip results I expected. No crazy procedure needed, hopefully these findings help someone out in the future.
    Attached Files Attached Files

Subscribe

Share this thread

Related Topics

  1. Helpful tips for testing Siemens SB-EC trip units (SBS circuit breakers)
    By SecondGen in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 27, 2021, 06:25 AM
  2. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 02:46 PM
  3. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  4. Easy way to calculate transformer fault current
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: June 11, 2015, 06:40 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net