VLF Test Ratings
    Jun 2018
    23
    VLF Test Ratings
    Hi guys,
    I need to perform VLF test on one set cable. The cable rating is 12/20 kV but opeation voltage is 15 kV. So what is the right VLF Test ratings for these cables?
    Thanks.
    Quote Originally Posted by changeabilities View Post
    Hi guys,
    Thanks.
Name:	IEEE 400.2 Table 3.png
    If the cable is rated for 20kV then I would say 26kV for Acceptance and 20kV for Maintenance as shown in the table above from IEEE 400.2.
    Jun 2018
    23
    And some of the cable has 6/10 cable rating but operating voltage is 1725 volts. And what is the correct voltage level for this cables?
  7. Kalbi_Rob's Avatar
    One thing I forgot to mention is to be aware of the termination and connected equipment as you should not exceed those ratings also.
    As for voltages to test at, they are all in the table.
    VLF is performed at the cable rating(or limiting component), and tan delta is based on operating voltage to ground.
  9. Kalbi_Rob's Avatar
    Oh, I guess to answer what the test voltage is when it is not on the table, requires a little more investigation on your part as you will have to find the manufacturer data on the cable to determine the test values.
  1. Circuit Breaker voltage ratings
    By nwilliams in forum NETA Level 3 Exam
    Last Post: February 12, 2021, 07:54 AM
  2. Most common rated insulation for control wiring
    By E-DivMafia in forum NETA Level 2 Exam
    Last Post: December 28, 2018, 08:15 AM