In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
The Doble book mainly talks about the bushings for this test, I took a quick look through a few VCB manuals and none of them mentioned PF testing as part of maintenance. I don't know that this is a standard factory test either, other than maybe the bushings which I imagine are PF tested individually at production? As far as I know we've never done this for a customer at our shop as part of any standard service.
Had this happen a few days ago, Power factored a medium voltage vac breaker and the test set could not recognize the leakage current because it was so low. Pretty much a pointless test.
-Justin
The only breakers I have used power factor testing for is oil field breakers. On vacuum breakers we just use the over potential test for vac integrity and insulation integrity. Things like this are interesting though. I'll have to do some research now.