Power Factor 15kV Vac Breakers

 Jump to latest post
    #1
  1. Join Date
    Oct 2015
    Posts
    5
    Reputation

    Power Factor 15kV Vac Breakers

    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by deloye4 View Post
    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
    The Doble book mainly talks about the bushings for this test, I took a quick look through a few VCB manuals and none of them mentioned PF testing as part of maintenance. I don't know that this is a standard factory test either, other than maybe the bushings which I imagine are PF tested individually at production? As far as I know we've never done this for a customer at our shop as part of any standard service.

  4. #3
  5. Join Date
    Oct 2015
    Posts
    5
    Reputation
    Quote Originally Posted by SecondGen View Post
    The Doble book mainly talks about the bushings for this test, I took a quick look through a few VCB manuals and none of them mentioned PF testing as part of maintenance. I don't know that this is a standard factory test either, other than maybe the bushings which I imagine are PF tested individually at production? As far as I know we've never done this for a customer at our shop as part of any standard service.
    These are for 15kV breakers. Manufacturers may not call it power factor tests, but that's the naming in the NETA book.

    Click image for larger version. 

Name:	Capture.JPG 
Views:	3 
Size:	34.0 KB 
ID:	308

  6. #4
  7. Join Date
    Jan 2015
    Posts
    10
    Reputation
    Quote Originally Posted by deloye4 View Post
    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
    We have had customers that required it for all vac bottle breakers, we showed they where it was listed as optional but they still wanted it. Doble has standards set for most Vac breakers however we have found that very few actually pass by doble standards.

  8. #5
  9. CEBrighton is offline Junior Member Pro Subscriber
    Join Date
    Feb 2019
    Posts
    3
    Reputation

    PF medium voltage breaker

    Had this happen a few days ago, Power factored a medium voltage vac breaker and the test set could not recognize the leakage current because it was so low. Pretty much a pointless test.
    -Justin

  10. #6
  11. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by deloye4 View Post
    These are for 15kV breakers. Manufacturers may not call it power factor tests, but that's the naming in the NETA book.

    Click image for larger version. 

Name:	Capture.JPG 
Views:	3 
Size:	34.0 KB 
ID:	308
    Hence the reason NETA always states test per "MANUFACTURER'S PUBLISHED DATA." I have only seen manufacturer's call for withstand and vacuum bottle integrity tests.

    Unfortunately, some customers want what they want and don't listen to reason.

  12. #7
  13. Join Date
    Aug 2018
    Posts
    7
    Reputation
    Quote Originally Posted by deloye4 View Post
    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
    Most manufacturers do not recommend power factor on vac or sf6 breakers. Most just high pot vac breakers but there is specialty equipment that use magnetic fields to measure vacuum.

  14. #8
  15. NBatson's Avatar
    NBatson is offline
    I NETA BREAK
    Junior Member
    Join Date
    Feb 2019
    Location
    TX Gulf Coast
    Posts
    19
    Reputation

    Vac Breakers

    The only breakers I have used power factor testing for is oil field breakers. On vacuum breakers we just use the over potential test for vac integrity and insulation integrity. Things like this are interesting though. I'll have to do some research now.

  16. #9
  17. Zog is offline Junior Member
    Join Date
    Oct 2014
    Posts
    15
    Reputation
    Quote Originally Posted by deloye4 View Post
    In the NETA ATS and MTS power factor testing for a medium voltage vac breaker is an optional test. I don't believe it is a recognized test by manufacturers. Does anyone have any documentation to back this up? Is it a typical test done by others?
    We have some customers that require it on Magneblast bushings but usually not the norm.

  18. #10
  19. Zog is offline Junior Member
    Join Date
    Oct 2014
    Posts
    15
    Reputation
    Quote Originally Posted by baccuskt View Post
    Most manufacturers do not recommend power factor on vac or sf6 breakers. Most just high pot vac breakers but there is specialty equipment that use magnetic fields to measure vacuum.
    The MAC test is now an optional test in both the ATS and MTS. Several utilities require it , we do it on every VCB we touch.

Subscribe

Share this thread

Related Topics

  1. Transformer Oil Pressure when Power Factor Testing
    By ElectricalTestTech in forum Electrical Testing Talk
    Replies: 8
    Last Post: October 3, 2020, 09:41 AM
  2. Power Factor for New Mineral Oil
    By Salcama in forum NETA Level 3 Exam
    Replies: 4
    Last Post: February 22, 2020, 05:12 PM
  3. Power factor testing mode of operation
    By E-DivMafia in forum NETA Level 2 Exam
    Replies: 1
    Last Post: October 31, 2018, 02:22 PM
  4. Replies: 9
    Last Post: August 16, 2018, 02:28 PM
  5. Replies: 7
    Last Post: May 28, 2018, 04:21 PM